[BLDG-SIM] Building additions and shading
Aulbach, John
jaulbach at nexant.com
Tue Jul 31 17:27:59 PDT 2007
Kevin:
I am getting a bit old and slow, so I don't quite understand your
questions.
If you are modeling a new construction rectangle that has both ends (say
top and bottom on a plan view) abutting existing structures, I believe
you can make these walls INTERIOR and ADIABATIC. In that way, you have
no outside influence on the wall, and no heat transfer to another space.
You WILL, however, need to make the changes in the .INP text file. You
simply cannot do it in the eQuest overlay.
Why do you care about shading from external sources. Just don't put
those sources In !!
Or have I missed something?
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Kevin
Kyte
Sent: Tuesday, July 31, 2007 9:15 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Building additions and shading
Greetings, I am simulating a building that from bird's eye view looks
like a big rectangle. Either end of the new construction is connected
to existing buildings. Furthermore, it appears the first floor of the
new construction extends into a renovation of one of the pre-existing
forms. How does one turn off shading on exterior surfaces? Also, would
it be better to modeling the existing buildings as well? The new
construction will be running on its own systems.
Thanks.
Kevin
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070731/702519ac/attachment-0002.htm>
More information about the Bldg-sim
mailing list