[BLDG-SIM] Multi-level zoning in eQuest
David S Eldridge
DSE at grummanbutkus.com
Mon Mar 19 12:36:28 PDT 2007
One question you (or anyone else) may ask yourself is how much difference it will make when you enter these different zones.
A) If you have a LEED building you should match the designed zones - lean towards detailed.
B) If this is a schematic design, and the scheduling and load density of people/lights/equipment of the departments between floors will not be much different - lean towards simplified.
If you are in the middle ground somewhere as will often be the case, then you'll have to decide whether to expend extra time modeling explicitly or using multipliers, or if you are going to need some specific output that you couldn't capture with multiplied floors and/or simplified zoning.
Hope this helps!
David
--------------------------------------------------------------
David S. Eldridge, Jr.
Project Engineer
LEED v2.0 Accredited Professional
Grumman/Butkus Associates
820 Davis St., Suite 300
Evanston, IL 60201
847.328.3555 ext. 224
dse at grummanbutkus.com
-------------------------------------------------------------
> -----Original Message-----
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf
> Of Alpana Jain
> Sent: Monday, March 19, 2007 1:49 PM
> To: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] Multi-level zoning in eQuest
>
> Please ignore my earlier mail regarding multi-level zoning! I
> ran a search and found the answer in a thread that dealt with
> this same issue almost an year ago!!
> Unless there is any other way of doing this, then please
> ignore my mail.
> Thanks
> Alpana
>
> -----Original Message-----
> From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf
> Of Rohini Brahme
> Sent: Thursday, January 19, 2006 11:28 AM
> To: bldg-sim at gard.com
> Subject: [bldg-sim] Multi-level zoning in eQuest
>
> since I just now was figuring out the same thing myself,
> thought I would share it. Here is what I did:
>
> use custom on all screens where needed. Each floor is a new
> shell. and on the next screen it asks for the placement of
> the shell - you can say immediately above/ below another shell.
>
> Hope this helps
> - Rohini
>
> --------------------------------------------
> Rohini Brahme
> Research Scientist
> Sustainable Technologies Group
> Houston Advanced Research Center
> 4800 Research Forest Drive
> The Woodlands, TX 77381
>
> Ph: 281-364-6006
> Fax: 281-364-6052
>
>
>
> -----Original Message-----
> From: bldg-sim at gard.com [mailto:bldg-sim at gard.com] On Behalf
> Of Gerald Pde
> Sent: Wednesday, January 18, 2006 9:01 AM
> To: bldg-sim at gard.com
> Subject: [bldg-sim] Multi-level zoning in eQuest
>
>
> The way I have handled multi level zoning is to build one
> floor at a time in the wizard and saving it as a different
> file. Then I manually go to the inp file and change all the
> names of the spaces and associated polygons and zones by
> doing a simple search and replace using textpad. Finally, I
> import the inp file of the second floor in the detailed interface.
> Hope this helps.
> Gerald
>
> --- Jeff Haberl <jeffhaberl at tees.tamus.edu> wrote:
>
> > I don't know if this is a useful exercise...since Equest's engine -
> > DOE-2 really works best with 5 zones per floor. Unless you're doing
> > something completely different in each zone (I.e. Changing
> thermostat
> > setpoints, or different sys types) I'm guessing it will have a
> > marginal impact beyond 5 zones per floor. In fact, 2 zone will
> > probably give good results for most buildings (inside,outside).
> > Several papers in the ASHRAE lit have addressed this issue.
> >
> > Jeff
> > BB 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) :=') 8=)
> > 8=) 8=? BB
> >
> > Jeff S. Haberl, Ph.D.,
> > P.E.............................jhaberl at esl.tamu.edu
> >
> >
> Professor......................................................Office
> > Ph: 979-845-6507
> >
> > Department of Architecture.......................Lab
> > Ph: 979-845-6065
> >
> > Energy Systems Laboratory.......................FAX:
> > 979-862-2457
> >
> > Texas A&M
> > University..............................77843-3581
> >
> > College Station, Texas,
> > USA.......................URL: www-esl.tamu.edu
> >
> > BB 8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) 8=? 8=)
> > 8=) 8= BB
> >
> >
> > -----Original Message-----
> > From: bldg-sim at gard.com <bldg-sim at gard.com>
> > To: bldg-sim at gard.com <bldg-sim at gard.com>
> > Sent: Tue Jan 17 11:12:58 2006
> > Subject: [bldg-sim] Multi-level zoning in eQuest
> >
> > Does anyone know if it’s possible to create different zoning
> > patterns per floor in the Design Wizard in eQuest?
> Manually, it can
> > be done in Detailed Data Edit mode, but I know I did it
> once before in
> > the wizard.
> >
> > Thanks,
> >
> > Kendra Tupper
> >
> > FLACK + KURTZ
> >
> > 405 Howard Street 415.398.3833 Main
> >
> > Suite 500 415.402.5840 Direct
> >
> > San Francisco, CA 94105 415.433.5311 Fax
> >
> > http://www.flackandkurtz.com
> > kendra.tupper at sf.fk.com
> > <mailto:kendra.tupper at sf.fk.com>
> >
> >
> >
> >
> >
> > This e-mail may contain confidential and/or privileged information.
> >
> > If you are not the intended recipient (or have received
> this e-mail in
> > error)
> >
> > please notify the sender immediately and destroy this e-mail.
> >
> > Any unauthorized copying, disclosure or distribution of the material
> >
> > in this e-mail is strictly forbidden.
> >
> >
> >
> >
> > ==================
> > You received this e-mail because you are subscribed to the
> > BLDG-SIM at GARD.COM mailing list. To unsubscribe from this
> mailing list
> > send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
> >
> >
>
>
> __________________________________________________
> Do You Yahoo!?
> Tired of spam? Yahoo! Mail has the best spam protection
> around http://mail.yahoo.com
>
> ======================================================
> You received this e-mail because you are subscribed to the
> BLDG-SIM at GARD.COM mailing list. To unsubscribe from this
> mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>
> ==================
> You received this e-mail because you are subscribed to the
> BLDG-SIM at GARD.COM mailing list. To unsubscribe from this
> mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
More information about the Bldg-sim
mailing list