[BLDG-SIM] eQuest Ventilation Loads & SIM File Oddities
Brandon Nichols
BrandonN at Hargis.biz
Wed May 23 11:34:32 PDT 2007
All,
Does anyone know which SIM file report summarizes outside air loads by
zone/system? Have searched the report for 'vent' and 'osa' (with 'match
case' unchecked) but found nothing.
Best of all would be a report that summarized all zone/system loads,
including ventilation air. The closest I found was "SS-B System Loads
Summary" and "SS-G Zone Loads Summary" but neither break-out
ventilation. You can also go to the 'Summary' tab in the eQuest GUI,
but that doesn't breakout ventilation either.
As to whether ventilation air energy is rolled into cooling and/or
heating numbers, I cannot tell because both of the these columns in the
SS-G report have all zeros in them, and every single value on the the
SS-B report is equal to zero!
Very curious, as I'm getting what I thought were reasonable numbers in
other parts of the SIM file, and in the graphical simulation output
reports. Does anyone know what the issue might be?
Thanks in Advance
Brandon Nichols, PE
Mechanical
HARGIS ENGINEERS
600 Stewart St
Suite 1000
Seattle, WA 98101
d | 206.436.0400 c | 206.228.8707
o | 206.448.3376 f | 206.448.4450
www.hargis.biz
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070523/5979bdbf/attachment.htm>
More information about the Bldg-sim
mailing list