[BLDG-SIM] eQuest Ventilation Loads & SIM File Oddities
Gerald Pde
geraldpde at yahoo.com
Wed May 23 14:08:19 PDT 2007
You can also run the model twice:
- Once with the actual envelope construction (walls,
roof glazing and infiltration)
- Second setting all envelope properties to zero
The difference will give you the approximate OA load
and energy consumption attributable to the OA.
Hope this helps,
Gerald
--- Brian Fountain <bfountain at greensim.com> wrote:
> A couple of things to look at:
>
>
>
> 1) The SV-A report gives you the OA % for each
> system
>
> 2) The reason your SS-G report has zeros is it
> is not a zonal
> system (Fan coils, PTACs) SS-G reports zonal energy
> rather than
> system energy - SS-A gives you the system cooling
> and heating energy.
>
> 3) You can look at the difference between the
> LS-B or LS-E
> reports which are internal and envelope loads
> without ventilation and
> the SS-I or SS-J reports which have ventilation to
> isolate ventilation
> energy.
>
>
>
> ____________________________________________
>
>
>
> -----Original Message-----
> From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com]
> On Behalf Of
> Brandon Nichols
> Sent: May 23, 2007 2:35 PM
> To: BLDG-SIM at gard.com
> Subject: [BLDG-SIM] eQuest Ventilation Loads & SIM
> File Oddities
>
>
>
> All,
>
>
>
> Does anyone know which SIM file report summarizes
> outside air loads by
> zone/system? Have searched the report for 'vent'
> and 'osa' (with
> 'match case' unchecked) but found nothing.
>
>
>
> Best of all would be a report that summarized all
> zone/system loads,
> including ventilation air. The closest I found was
> "SS-B System Loads
> Summary" and "SS-G Zone Loads Summary" but neither
> break-out
> ventilation. You can also go to the 'Summary' tab
> in the eQuest GUI,
> but that doesn't breakout ventilation either.
>
>
>
> As to whether ventilation air energy is rolled into
> cooling and/or
> heating numbers, I cannot tell because both of the
> these columns in
> the SS-G report have all zeros in them, and every
> single value on the
> the SS-B report is equal to zero!
>
>
>
> Very curious, as I'm getting what I thought were
> reasonable numbers in
> other parts of the SIM file, and in the graphical
> simulation output
> reports. Does anyone know what the issue might be?
>
>
>
>
>
> Thanks in Advance
>
>
>
> Brandon Nichols, PE
> Mechanical
> HARGIS ENGINEERS
> 600 Stewart St
> Suite 1000
> Seattle, WA 98101
> d | 206.436.0400 c | 206.228.8707
> o | 206.448.3376 f | 206.448.4450
> www.hargis.biz
>
>
>
> ==================
> You received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To
> unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
>
>
>
=====================================================You
> received this e-mail because you are subscribed
> to the BLDG-SIM at GARD.COM mailing list. To
> unsubscribe
> from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at GARD.COM
____________________________________________________________________________________You snooze, you lose. Get messages ASAP with AutoCheck
in the all-new Yahoo! Mail Beta.
http://advision.webevents.yahoo.com/mailbeta/newmail_html.html
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list