[BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case
Michael Rosenberg
Michael.Rosenberg at state.or.us
Wed May 16 10:47:02 PDT 2007
The requirement to distribute fenestration uniformly in horizontal
bands across the four orientations has been removed from Appendix G in
the published Addenda Supplement to 90.1, 2004. See the ASHRAE website
for the supplement.
http://www.ashrae.org/technology/page/132
Michael Rosenberg
Oregon Department of Energy
625 Marion St. N.E.
Salem, OR 97301-3742
Phone : (503) 373-7809
Fax: (503) 373-7806
>>> Chris Jones <cj at cr-jay.ca> 5/16/2007 9:56:02 AM >>>
Appendix G notes that for the Baseline building: "Vertical
fenestration areas for new buildings and additions shall equal that
in the proposed design or 40% of gross above grade wall area,
whichever is smaller, and shall be distributed uniformly in
horizontal bands across the four orientations."
Does this mean that the Baseline building gets windows on all walls
on each orientation whether or not the Design case has a window in
all walls on each orientation. For example, if the west orientation
has 30% glazing overall but many spaces have no windows - some walls
on the west face have more that 30%. Do those spaces in the Baseline
case get 30% glazing? Or do I only put windows in the Baseline case
where there are windows in the Design case.
Thanks for any help!
Chris Jones, P.Eng.
14 Oneida Avenue
Toronto, ON M5J2E3
Tel. 416 203-7465
Fax. 416 946-1005
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list