[BLDG-SIM] charlottesville, VA - design temp
Mahabir Bhandari
Bhandari at DesignBuildersoftware.com
Fri May 4 12:08:17 PDT 2007
Alpana,
The nearest weather file is available for Lynchburg, VA with
CDD50 = 3722
HDD65=4305
And the design data are (source: the weather file from E+ website):
DesignDay,
LYNCHBURG Ann Htg 99.6% Condns DB, !- Name
-10.7, !- Max Dry-Bulb {C}
0.0, !- Daily Temp Range {C}
-10.7, !- Humidity Indicating Condition at Max Dry-Bulb
98018., !- Barometric Pressure {Pa}
2.8, !- Wind Speed {m/s} design conditions vs. traditional 6.71
m/s (15 mph)
310, !- Wind Direction {Degrees; N=0, S=180}
0.00, !- Clearness {0.0 to 1.1}
0, !- Rain {0-no,1-yes}
0, !- Snow on ground {0-no,1-yes}
21, !- Day of Month
1, !- Month
WinterDesignDay,!- Day Type
0, !- Daylight Savings Time Indicator
Wet-Bulb; !- Humidity Indicating Type
! LYNCHBURG_VA_USA Annual Heating 99%, MaxDB=-8°C
DesignDay,
LYNCHBURG Ann Htg 99% Condns DB, !- Name
-8, !- Max Dry-Bulb {C}
0.0, !- Daily Temp Range {C}
-8, !- Humidity Indicating Condition at Max Dry-Bulb
98018., !- Barometric Pressure {Pa}
2.8, !- Wind Speed {m/s} design conditions vs. traditional 6.71
m/s (15 mph)
310, !- Wind Direction {Degrees; N=0, S=180}
0.00, !- Clearness {0.0 to 1.1}
0, !- Rain {0-no,1-yes}
0, !- Snow on ground {0-no,1-yes}
21, !- Day of Month
1, !- Month
WinterDesignDay,!- Day Type
0, !- Daylight Savings Time Indicator
Wet-Bulb; !- Humidity Indicating Type
! LYNCHBURG_VA_USA Annual Humidification 99.6% Design Conditions DP=>MCDB,
DP=-20.7°C
DesignDay,
LYNCHBURG Ann Hum_n 99.6% Condns DP=>MCDB, !- Name
-6.7, !- Max Dry-Bulb {C}
0.0, !- Daily Temp Range {C}
-20.7, !- Humidity Indicating Condition at Max Dry-Bulb
98018., !- Barometric Pressure {Pa}
2.8, !- Wind Speed {m/s} design conditions vs. traditional 6.71
m/s (15 mph)
310, !- Wind Direction {Degrees; N=0, S=180}
0.00, !- Clearness {0.0 to 1.1}
0, !- Rain {0-no,1-yes}
0, !- Snow on ground {0-no,1-yes}
21, !- Day of Month
1, !- Month
WinterDesignDay,!- Day Type
0, !- Daylight Savings Time Indicator
Dew-Point; !- Humidity Indicating Type
! LYNCHBURG_VA_USA Annual Humidification 99% Design Conditions DP=>MCDB,
DP=-17.8°C
DesignDay,
LYNCHBURG Ann Hum_n 99% Condns DP=>MCDB, !- Name
-4.2, !- Max Dry-Bulb {C}
0.0, !- Daily Temp Range {C}
-17.8, !- Humidity Indicating Condition at Max Dry-Bulb
98018., !- Barometric Pressure {Pa}
2.8, !- Wind Speed {m/s} design conditions vs. traditional 6.71
m/s (15 mph)
310, !- Wind Direction {Degrees; N=0, S=180}
0.00, !- Clearness {0.0 to 1.1}
0, !- Rain {0-no,1-yes}
0, !- Snow on ground {0-no,1-yes}
21, !- Day of Month
1, !- Month
WinterDesignDay,!- Day Type
0, !- Daylight Savings Time Indicator
Dew-Point; !- Humidity Indicating Type
! LYNCHBURG_VA_USA Annual Heating Wind 99.6% Design Conditions WS=>MCDB,
WS=9.8m/s
DesignDay,
LYNCHBURG Ann Htg Wind 99.6% Condns WS=>MCDB, !- Name
2.6, !- Max Dry-Bulb {C}
0.0, !- Daily Temp Range {C}
2.6, !- Humidity Indicating Condition at Max Dry-Bulb
98018., !- Barometric Pressure {Pa}
9.8, !- Wind Speed {m/s} design conditions vs. traditional 6.71
m/s (15 mph)
310, !- Wind Direction {Degrees; N=0, S=180}
0.00, !- Clearness {0.0 to 1.1}
0, !- Rain {0-no,1-yes}
0, !- Snow on ground {0-no,1-yes}
21, !- Day of Month
1, !- Month
WinterDesignDay,!- Day Type
0, !- Daylight Savings Time Indicator
Wet-Bulb; !- Humidity Indicating Type
! LYNCHBURG_VA_USA Annual Heating Wind 99% Design Conditions WS=>MCDB,
WS=8.8m/s
DesignDay,
LYNCHBURG Ann Htg Wind 99% Condns WS=>MCDB, !- Name
3, !- Max Dry-Bulb {C}
0.0, !- Daily Temp Range {C}
3, !- Humidity Indicating Condition at Max Dry-Bulb
98018., !- Barometric Pressure {Pa}
8.8, !- Wind Speed {m/s} design conditions vs. traditional 6.71
m/s (15 mph)
310, !- Wind Direction {Degrees; N=0, S=180}
0.00, !- Clearness {0.0 to 1.1}
0, !- Rain {0-no,1-yes}
0, !- Snow on ground {0-no,1-yes}
21, !- Day of Month
1, !- Month
WinterDesignDay,!- Day Type
0, !- Daylight Savings Time Indicator
Wet-Bulb; !- Humidity Indicating Type
! LYNCHBURG Annual Cooling Design Conditions Wind Speed=3.6m/s Wind Dir=240
! Hottest Month=JUL
! LYNCHBURG_VA_USA Annual Cooling (DB=>MWB) .4%, MaxDB=33.4°C MWB=23.4°C
DesignDay,
LYNCHBURG Ann Clg .4% Condns DB=>MWB, !- Name
33.4, !- Max Dry-Bulb {C}
10.7, !- Daily Temp Range {C}
23.4, !- Humidity Indicating Condition at Max Dry-Bulb
98018., !- Barometric Pressure {Pa}
3.6, !- Wind Speed {m/s} design conditions vs. traditional 3.35
m/s (7mph)
240, !- Wind Direction {Degrees; N=0, S=180}
1.00, !- Clearness {0.0 to 1.1}
0, !- Rain {0-no,1-yes}
0, !- Snow on ground {0-no,1-yes}
21, !- Day of Month
7, !- Month
SummerDesignDay,!- Day Type
0, !- Daylight Savings Time Indicator
Wet-Bulb; !- Humidity Indicating Type
! LYNCHBURG_VA_USA Annual Cooling (DB=>MWB) 1%, MaxDB=31.9°C MWB=22.9°C
DesignDay,
LYNCHBURG Ann Clg 1% Condns DB=>MWB, !- Name
31.9, !- Max Dry-Bulb {C}
10.7, !- Daily Temp Range {C}
22.9, !- Humidity Indicating Condition at Max Dry-Bulb
98018., !- Barometric Pressure {Pa}
3.6, !- Wind Speed {m/s} design conditions vs. traditional 3.35
m/s (7mph)
240, !- Wind Direction {Degrees; N=0, S=180}
1.00, !- Clearness {0.0 to 1.1}
0, !- Rain {0-no,1-yes}
0, !- Snow on ground {0-no,1-yes}
21, !- Day of Month
7, !- Month
SummerDesignDay,!- Day Type
________________________________________
From: neeraj [mailto:near_ej at yahoo.com]
Sent: Friday, May 04, 2007 1:54 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] charlottesville, VA - design temp
Does anyone know the heating cooling design temperature for Charlottesville,
VA?
Thanks
Alpana
________________________________________
Ahhh...imagining that irresistible "new car" smell?
Check out new cars at Yahoo! Autos.
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
More information about the Bldg-sim
mailing list