[BLDG-SIM] LEED credit for reduced infiltration?
    Michael Tillou 
    michael.tillou at gmail.com
       
    Tue Nov 20 12:14:07 PST 2007
    
    
  
Karen,
Chapter 11 of ASHRAE 90.1-2004 and Appendix G do not allow any credit for
reduced infiltration in commercial buildings.  
It is my understanding that there isn't enough data to form a consensus on
what the baseline would/should be.  Not to mention the challenge of blower
door testing a large commercial project and getting consistent results..  
If you look at the Residential Systems Approach in the IECC 2006 you will
see that there is a method for claiming credit for reduced infiltration on
residential projects.  The baseline they establish is based on Normalized
Leakage of .57 and the weather factor W for the project site from ASHRAE
Standard 136.  IECC does not allow credit for infiltration rates lower than
0.35 ACH.
Mike   
Michael Tillou, PE, LEED
Tillou Engineering, LLC
Williamstown, MA 01267
P: 413-458-9870 C: 413-652-1087
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Karen
Walkerman
Sent: Tuesday, November 20, 2007 8:42 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] LEED credit for reduced infiltration?
Hello again,
I'm modeling a couple projects, one currently under LEED 2.1 (ECB) and a few
under LEED 2.2 (Appendix G).  To date, I have not seen any mention of
infiltration.  If the envelope is tested, can credit be taken for reduced
infiltration in the proposed design?  If so, what's the baseline?  For
renovated buildings can a pre-construction blower door test be the baseline?
Thanks!
--
Karen Walkerman
Second Law Consulting
======================================================
You received this e-mail because you are subscribed to the BLDG-SIM at GARD.COM
mailing list.  To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
    
    
More information about the Bldg-sim
mailing list