[BLDG-SIM] Occupancy Sensors
    Kingsley, Michael L. 
    MICHAEL.L.KINGSLEY at saic.com
       
    Fri Nov 16 13:07:15 PST 2007
    
    
  
Steve,
For reference, ASHRAE 90.1-2004, Appendix G (Performance Rating Method)
allows by default a 10% reduction (see Table G3.2 for qualifiers) in
lighting power density for areas that incorporate occupancy sensor
control of lighting.  Note that the Standard does mandate automatic
lighting controls for certain spaces (classrooms, conference/meeting
rooms, lunch/break rooms), so no credit is allowed for these areas.
Alternatively, the Standard can still be met by altering the schedules
if "credible technical documentation for the modifications are
provided".
If this is a LEED project then the above gudelines should be followed,
otherwise they do serve as a defensible rationale for dealing with
occupancy sensor controls.
Michael L. Kingsley, PhD, PE, LEED AP
Senior Engineer/ Project Manager
SAIC
6390 Fly Road
East Syracuse, New York 13057
-----Original Message-----
From: postman at gard.com [mailto:postman at gard.com] On Behalf Of stobin
Sent: Friday, November 16, 2007 3:32 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Occupancy Sensors
Has anyone tried to model occupancy sensors for the lighting system in
E-Quest?
 
I have a rather large building (135,000 sq ft) inwhich 30% or so is
opperated 24/7 and the rest is a typical office building.  We are
including occupancy sensors in each room but we are unsure how to
quantify the savings those sensors may provide.  The only way I
understand to show savings is to reduce the lighting schedules, but I do
not know how much.  I am finding that lighting is approximately 30% to
35% of total building energy consumption and savings here could mean a
decent cost savings.  Has any one had any experiance with this?  I would
appreciate any help you can give me.
 
Thanks
 
Steve Tobin, E.I.T.
PROJECT ENGINEER
Smith & Boucher Engineers
25501 west valley parkway
olathe ks 66061
direct 913 344.0061 
fax 913 345.0617
 
 
==================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
    
    
More information about the Bldg-sim
mailing list