[BLDG-SIM] Appendix G Supply Fan Power
    Zarske, Jim 
    jzarske at nexant.com
       
    Thu Nov 15 14:38:42 PST 2007
    
    
  
I've interpreted Appendix G that they fan sizing is for the baseline
building only; use actual fan sizes for the proposed building.
The fan sizing run should only apply to the 8 predefined system options
in Appendix G for your building type.  So, if you're taking one of these
defined systems that applies to your building and modeling it on each of
your proposed spaces, you would have to do a sizing run for each system.
The sizing run should be at the HVAC system level.
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Karen
Walkerman
Sent: Thursday, November 15, 2007 2:57 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Appendix G Supply Fan Power
Hi All,
Question about ASHRAE 90.1 Appendix G3.1.2.9 (calculation for fan energy
use):
does this apply only to the baseline model?  I assume that actual fan
power should be used for the proposed design, but ASHRAE doesn't state
it explicitly.
Also, should fan power use be calculated for each space served by an
independent system, or for the whole building?
I am modeling a building that is supplied with baseboard heat, and no
cooling.  There are a number of small offices that have independent
thermostats for heating.  As per LEED requirements, these spaces must be
modeled as having mechanical cooling.  Some of the spaces only require
2-300 cfm of supply air.  If I do the calculation for each space, I end
up with 8 watts/cfm!!!  (can't be right)
Thanks for any input,
~Karen~
--
Karen Walkerman
Second Law Consulting
kwalkerman at gmail.com
======================================================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list.  To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
    
    
More information about the Bldg-sim
mailing list