[BLDG-SIM] eQUEST error message
Kristin Field
KField at archenergy.com
Wed Oct 31 13:24:24 PDT 2007
Check the PS-C or PS-D report to see which piece of equipment is
overloaded. That will help you diagnose what is going on in your
central plant.
***************************************************************
Kristin M. Field, EI
Energy Analysis Group
Architectural Energy Corporation
2540 Frontier Ave., Suite 201
Boulder, CO 80301
303.444.4149
>>> "Seth P. Spangler" <sspangle at rmf.com> 10/31/2007 12:39 PM >>>
Hello,
I am trying to “fix” an eQUEST model a co-worker of mine started. I get
this error message for every zone that was created. Can anyone tell me
what it references or what is causing the error?
System: EL1 Sys7 (SZRH) (G.WNW2) could not successfully
allocate all energy to the 5-minute bins during
heating because of an equipment overload. The peak
load used in ECONOMICS will not include the fraction
due to the overload, but the PLANT reports will.
Mon/Day/Hour: 6 15 1 Energy: 8.9 Unallocated: 0.135
Thanks in advance for your help.
Seth Spangler, LEED® AP
Design Engineer
RMF Engineering, Inc
Ph: (843) 971-9639 ext:108
Fax: (843) 971-9641
sspangle at rmf.com
=====================================================You received this
e-mail because you are subscribed to the BLDG-SIM at GARD.COM mailing list.
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071031/7731a30a/attachment-0002.htm>
More information about the Bldg-sim
mailing list