[BLDG-SIM] New Calculation method for Baseline Fan Energy in Addendum R
Leader, Philip
Philip.Leader at akahn.com
Wed Oct 24 12:12:25 PDT 2007
I'd agree with you Mike.
Addendum r revised the reference standard for ARI 340/360 from the 2000
version to the 2004 version in Section 12 Normative References.
By the way, the older 1989 version of Standard 90.1 had it right in the
first place using Brake HP and not motor nameplate HP for the fan power
limit. It only took them about 18 years to realize they had a problem.
Better late than never.
Also the added credits or adjustment factors were long overdue too.
Philip S. Leader, PE
Director of Mechanical Engineering
Albert Kahn Associates, Inc.
7430 Second Ave.
Detroit, Michigan 48202-2798
P: 313.202.7834
F: 313.202.7334
E: philip.leader at akahn.com
www.albertkahn.com
Albert Kahn Family of Companies, founded in 1895
Architecture, Engineering, Planning, Design and Management
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Michael
Tillou
Sent: Wednesday, October 24, 2007 2:39 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] New Calculation method for Baseline Fan Energy in
Addendum R
I think you mean to be referencing ASHRAE 90.1-2004 addendum ac not
addendum r which includes two new methods for calculating fan power
limits. The first looks at total Motor HP which isn't very useful for
energy modeling purposes and the second looks at fan brake-horsepower.
The fan brake-horsepower equations are "(CFM x 0.00094) + A" and "(CFM
x 0.0013) + A" for constant volume and variable volume systems
respectively. CFM is the design airflow rate and A is the brakehorse
power adjustement for various pressure drop adjustments given in Table
6.5.3.1.1B.
Mike
Michael Tillou, PE, LEED
Tillou Engineering, LLC
Williamstown, MA 01267
P: 413-458-9870 C: 413-652-1087
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Andrew
Craig
Sent: Wednesday, October 24, 2007 11:56 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] New Calculation method for Baseline Fan Energy in
Addendum R
I was wondering if anyone out there can explain the new calculation
shown for baseline fan brake horsepower in Table G3.1.2.9 of Addendum R
to ASHRAE 90.1-2004? At first glance, the equation doesn't make sense
because you are subtracting a relatively small number (0.0013+A) from a
large number (CFMs) leaving you with a ridiculously large baseline fan
motor brake horsepower. Am I just reading this wrong or is there a
typo? Isn't there an easier way out there to calculate baseline fan
energy (please see version 1 of Appendix G for another confusing
calculation)?
Andrew Craig, EIT, LEED(r) AP | Mechanical Designer
INTERFACE ENGINEERING
708 SW Third Avenue | Suite 400 | Portland, OR 97204
direct: 503.382.2696
office: 503.382.2266
fax: 503.382.2262
email: Andrew_C at ieice.com
web: www.ieice.com
Consultants of Choice to the Built Environment for over 35 years
Kirkland, WA | Portland, OR | Sacramento, CA | Salem, OR | SanFrancisco,
CA
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
This email message and any attachments are intended only for the use of the addressee(s) named above. This message may contain privileged and confidential information, and may be protected by copyright. If you are not the intended recipient, any review, dissemination, distribution or copying is strictly prohibited. If you received this email message in error, please immediately delete it and notify the sender by replying to this email, or by telephone. Thank you.
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071024/3061f208/attachment-0002.htm>
More information about the Bldg-sim
mailing list