[BLDG-SIM] Air Cooled Chiller Performance Curve
Ian Doebber
Ian.Doebber at arup.com
Mon Sep 10 23:00:38 PDT 2007
For the Chiller EIR input, below is the equation to calculate the EIR
based on the Part Load Ratio. I am modeling air cooled chillers.
What is "r1" and "dT" refer to? I'm assuming that "r1" is the actual
cooling load divided by the maximum cooling capacity based on the
condenser temperature (ambient dry bulb temperature) and "dT" is the
difference between the chilled water supply and return temperature
(which is 10 with 44 supply and 54 return). I'm getting numbers that
are extremely low especially for low PLRs. I would think that the
maximum efficiency would be around 40-60% PLR but am not seeing this.
BI-QUADRATIC-RATIO&dT The curve is bi-quadratic in 2 independent
variables. It has the form
f(r1,dT) = c1 + c2*r1 + c3*r12 + c4*dT
+ c5*dT2 + c6*r1*dT,
where c1, c2, c3, c4, c5, and c6 are
coefficients. R1 is a dimensionless variable. dT is a variable with
units of delta temperature.
Ian
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070910/b0079f85/attachment.htm>
More information about the Bldg-sim
mailing list