[BLDG-SIM] eQUEST: Central Chiller for Baseline?

Sam Mason sam.mason at a10nyc.com
Tue Sep 25 06:30:58 PDT 2007


Yoko,

In note 5 under Table 11.3.2A, 90.1-2004 says for systems using
purchased chilled water, no chillers shall be modeled and CHW costs
shall be determined using the adopting authority's utility rates.  For
both the baseline and proposed buildings, you would not include central
chillers and instead use purchased chilled water.

 

Sam

 

--
Sam Mason
Atelier Ten
sam.mason at atelierten.com
  

________________________________

From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Yoko
Matsuyama
Sent: Monday, September 24, 2007 8:09 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] eQUEST: Central Chiller for Baseline?

 

Hi, everyone,

 

I am modeling a building that is served chilled water from a central
chiller, and the building doesn't have any individual chiller. 

I am wondering if  the baseline model (by ASHRAE 90.1-2004) should
follow ASHRAE specified "type and number of chillers" (TABLE G3.1.3.7,
ASHRAE 90.1-2004) depending on building conditioned floor area, or it
should be modeled with a Central chiller as proposed/designed model.  

 

Thank you for your help

 

 

YM 

Graduate Mechanical Engineer



===========================
You received this e-mail because you are subscribed 
to the BLDG-SIM at GARD.COM mailing list.  To unsubscribe 
from this mailing list send a blank message to 
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070925/8d49d998/attachment-0002.htm>


More information about the Bldg-sim mailing list