[BLDG-SIM] baseline system
Vamshi Gooje
vamshi.gooje at gmail.com
Wed Sep 12 09:51:00 PDT 2007
i think in either case you would be using system 5.
table g3.1.1a of appendix G, recommends using system 5 for non
residential buildings that are 5 floors or less & between 75000
-150000 SF. i believe it should read 5 floors or more instead of 5
floors or less. there is more clarity in the user manual on page
G-23. I would check the errata sheet to be double sure.
- Vamshi
On Sep 12, 2007, at 11:30 AM, Bill Talbert wrote:
> In Table G3.1.1A, the baseline building system is selected based on
> building area and the number of floors. Does anyone know if a
> Penthouse is considered a floor? From the A90.1 definitions, it
> appears that the Penthouse should be included in the gross floor
> area, but whether the Penthouse should be considered in defining
> the baseline building system type is unclear. For a 120,000 SF
> building that has 5 floors and a Penthouse and purchased heat, the
> baseline system could be System 5 if the Penthouse is not counted
> as a floor or System 7 if the Penthouse is included. Can anyone
> help clarify this?
> Thanks,
> Bill Talbert
>
> ======================================================