[BLDG-SIM] Question about Inputting COP and SEER values in Detailed Data Edit Mode
Brian Fountain
bfountain at greensim.com
Tue Sep 11 06:57:13 PDT 2007
EIR can definitely be changed in the detailed mode, and also in
parametric runs.
COP is converted into "Cooling Electric Input Ratio" or EIR values for
both chillers and for DX cooling. (See basic chiller screen and
cooling-unitary power screen)
EIR = 1/COP
EIR = 1/(EER/3.413)
____________________________________________
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Jeremy
Plitt
Sent: September 11, 2007 9:25 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Question about Inputting COP and SEER values in
Detailed Data Edit Mode
I was wondering if anyone knew how to input COP and SEER values in the
Detailed Data Edit Mode? I am comparing design variations for a
building and am just changing the values from the first file rather
than inputting everything all over again in a new file. Can I change
the COP and SEER values in the Detailed Data Edit Mode or do I have to
go back to the Building Creation Wizard to accomplish this?
Thanks,
Jeremy Plitt
Mechanical Engineer
Setty & Associates, Ltd.
3040 Williams Drive Suite 600
Fairfax, VA 22031-4618
PH: 703-691-2115 Ext. 123
FX: 703-691-8084
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070911/af667532/attachment-0002.htm>
More information about the Bldg-sim
mailing list