[Bldg-sim] VAV zone/Daylighting/DCV questions...
Eric Youngson
ericy at pae-engineers.com
Wed Apr 30 11:41:58 PDT 2008
Josh,
1. I would say that you should create a separate zone for each
terminal unit, especially if it has a FPB. Even if the exposure has the
same, the internal loads may be different.
2. Yes. BUILDING SHELL, Space properties, Daylighting tab
3. Yes. AIR-SIDE-HVAC, System properties, Outdoor Air tab, Outdoor
Ventilation Air; Minimum OA Sizing Method - Select DCV Return Sensor
(See attached file)
Good luck!
<http://www.pae-engineers.com/>
Eric Youngson
PAE Consulting Engineers, Inc.
503.226.2921 Main
503.542.0567 Direct
503.226.2930 Fax
ericy at pae-engineers.com
Mechanical
808 SW Third Avenue - Suite 300
Portland, OR 97204-2426
www.pae-engineers.com
inspire interpret integrate
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Josh
Greenfield
Sent: Friday, April 25, 2008 9:29 AM
To: equest-users at lists.onebuilding.org; bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] VAV zone/Daylighting/DCV questions...
eQuest Newbie question 1...When creating a building in eQuest that is
served by VAV and Fan-Powered Boxes, is it suggested that I create a
'zone' (using the wizard) for every single zone in the building that is
served by an individual VAV or FPB or should the zones be based purely
on similar exposures??
eQuest Newbie question 2...In the detailed edit mode, can I just have
one zone have daylight lighting controls while the other zones in the
system have generic lighting controls? If so, how and where do I do
that?
eQuest Newbie question 3...In the detailed edit mode also, can I just
have one zone have Demand Control Ventilation while the other zones in
the system have a constant minimum OA value? If so, how and where do I
do that?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080430/258eae4f/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2029 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080430/258eae4f/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 143 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080430/258eae4f/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Demand Control Ventilation - Madison.pdf
Type: application/octet-stream
Size: 186861 bytes
Desc: Demand Control Ventilation - Madison.pdf
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080430/258eae4f/attachment-0001.obj>
More information about the Bldg-sim
mailing list