[Bldg-sim] Spam:Re: LEED NC Submittal Template, Heating/Cooling Hours Loads Not Met
Carol Gardner
gems at spiritone.com
Thu Aug 21 23:43:41 PDT 2008
I have always looked at the SS-F report. Does any one else use it?
Michael Tillou wrote:
> If you're using eQuest the Air Side Summary report in the eQuest interface
> has all that info. It is also reported in SS-R Zone Performance Summary in
> the .SIM file.
>
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jay Keazer
> Sent: Thursday, August 21, 2008 5:16 PM
> To: Dan Russell; Brandon Nichols; bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] Spam:Re: LEED NC Submittal Template,Heating/Cooling
> Hours Loads Not Met
>
> I am not certain, but I think the unmet load hours on the BEPS report is
> consistent with the definition in Addendum a. The BEPS report says "Percent
> of hours any system zone outside of throttling range." To me this is the
> same as "one or more zones" being out of range for a particular hour.
>
> Adding up the unmet load hours of every zone would count a lot of coincident
> unmet hours and could get large with a lot of systems (note this is what
> SS-R does for multiple zone systems). It could be greater than 8760, and I
> don't think this is what appendix G is looking for. If a lot of zones are
> out of range during an hour (say an exceptionally cold night) that should
> only count as 1 hour.
>
> I don't think that the number on the BEPS is for the "worst case zone." I
> just checked a SIM file I had open and the BEPS report listed 3.3% unmet
> load hours, so 289 hours (actually anywhere from 285-293). Looking through
> SS-R for each zone, the worst case had 177 hours under heated + 24 hours
> under cooled, so 201 total unmet hours.
>
> I have always gone by the BEPS (i.e. 3.4% or less is good), but have never
> known how to find more detailed output regarding how many are cooling vs.
> how many are heating. Theoretically I think you could do this with an
> hourly report for every zone and some postprocessing, but I don't really
> want to go there. Anybody have a more practical approach?
>
>
> Jay Keazer, EI
> Energy Engineer
> TME, Inc.
> 2039 N Green Acres Road
> Fayetteville, AR 72703
>
> ph 479.521.8634
> fax 479.521.1014
> jkeazer at tmecorp.com
> www.tmecorp.com
>
>
>
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dan Russell
> Sent: Thursday, August 21, 2008 1:12 PM
> To: Brandon Nichols; bldg-sim at lists.onebuilding.org
> Subject: Spam:Re: [Bldg-sim] LEED NC Submittal Template,Heating/Cooling
> Hours Loads Not Met
>
> Brandon, I have been on the same page regarding this issue, and have
> submitted for successful LEED certifications using those assumptions ...
> until I read Addendum a to 90.1-2004, which adds the definition of "unmet
> load hour" to Section 3.2. The definition is:
>
> unmet load hour: an hour in which one or more zones is outside of the
> thermostat setpoint range.
>
> Unfortunately this seems to clearly indicate the unmet load hour value asked
> for refers to all zones at once.
>
> My previous assumptions to only consider the worst-case zone were based on
> the example set forth by the USGBC's document titled "Example LEED-NC
> v2.1 Energy & Atmosphere Credit 1 Submittal", which I referenced back when I
> did my first LEED submittal in 2005. This document is still available from
> their server at the following address:
>
> http://www.usgbc.org/ShowFile.aspx?DocumentID=2423
>
> This document uses the following paragraph to demonstrate compliance with
> the unmet load hour requirement:
>
> "The worst-case zone in the budget case is a North classroom. This zone is
> under-heated 40 hours out of the year in the Energy Cost Budget case and 0
> hours per year in the Design Energy Cost case. This is within the 50 hour
> per year limit required by ASHRAE 90.1-1999."
>
> Now, if Addendum a were not used in any part as basis for LEED submittal one
> could possibly argue using the quoted precedent above. Granted, the above
> precedent applied to the 1999 version of 90.1 and the 2.1 version of LEED,
> but it seems to reasonable that the implications made there should carry
> over until otherwise directed (as in Addendum a).
> Furthermore, it is my opinion that 90.1-2004 (not including addendums) does
> not clearly resolve the issue. The ASHRAE technical committee must have
> agreed, hence the inclusion of the new definition for "unmet load hour" in
> Addendum a.
>
> So, if Addendum a is not used, there may be a possibility to consider unmet
> load hour only on a worst-zone basis. However, if Addendum a is used it
> seems clear that the unmet load hour applies to all zones at once.
>
> Certainly larger project simulations with multiple zones will suffer from
> this added definition.
>
> Thanks,
>
> Dan Russell, EIT
>
>
>
>
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org
> [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Brandon Nichols
> Sent: Thursday, August 21, 2008 11:22 AM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] LEED NC Submittal Template,Heating/Cooling Hours Loads
> Not Met
>
>
> All,
>
> "Table 1.3 -- Advisory Messages" of the LEED NC Submittal Template requests
> "number of hours heating loads not met" and "number of hours cooling loads
> not met". We've taken a vote here in the office, and its 2-0 in favor of
> reporting the worst case zone as shown on the BEPS report.
>
> But we have some lingering doubts... can anyone say definitively what
> numbers are being asked to for here? our runner-up in the voting was the
> total of all zone hours out of throttling range -- however this could easily
> exceed the limit of 300 hours on a large project with many zones.
>
> As 300 hours is less than 5% (3.4% actually) of 8760, we think that the 300
> hours is "per zone", not a total limit for the entire project.
>
> Comments appreciated....
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
More information about the Bldg-sim
mailing list