[Bldg-sim] Ground Source Heat Exchanger in eQUEST
Potipireddi, Aditya
Aditya.Potipireddi at stantec.com
Fri Dec 12 17:08:22 PST 2008
Hi All,
I was wondering if any one could share their thoughts on the modeling approach in equest for the following HVAC system .
A typical unit, at the zone level there is a 4 pipe FC unit with chilled water from a Air Cooled Scroll Chiller and hot water coming for a heat exchanger. the heat exchanger it self is getting it hot water from a central geothermal plant . there is no boiler in this system.
here are couple of approaches I tried.
Approach 1: Demand side--model a Water loop HP with lake/well as source and connect the loop to hot water coils (without the boiler), and for cooling, to represent a scroll chiller, model a Screw chiller and connect that to a CHW loop which finally connects to the cooling coils. Supply side-- 4 pipe fan coil unit.
Although what I just described represents closely to my actual system, I could not do it with out boiler on the demand side, moreover I had other loop connection errors both on the demand side and supply side.
Approach 2: Demand side--Model a HW boiler connect to a hot water loop and a Screw chiller connected to a chilled water loop , Supply side--- 4 Pipe FC unit. tweak the boiler parameters to fake a geothermal system in terms of loop temp and efficiency, which would be 100% . and put the boiler on a separate meter to deduct the boiler energy use(kw) in the end from the total annual energy use.
To a certain extent I am convinced that approach 2 would work. but I wanted to throw these ideas on the table to hear your comments and any new ways to model this above discussed HAVC system.
Thank you for your time and valuable suggestion.
Aditya Potipireddi
Sustainable Building Analyst
Stantec
1932 First Avenue Suite 307
Seattle WA 98101
Ph: (206) 770-7770
Fx: (206) 770-5941
Aditya.Potipireddi at stantec.com
stantec.com
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
* Please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20081212/e16c7e78/attachment.htm>
More information about the Bldg-sim
mailing list