[Bldg-sim] ASHRAE 90.1 & Shading from adjacent buildings
C. J. Gann
cjg04austin at swbell.net
Wed Feb 27 07:10:05 PST 2008
Amanda,
P. G-14 in the ASHRAE 90.1-2004 User's Manual states that "self-shading" (in
the case of an L-shaped building for instance) is ignored in the baseline
building but credited to the proposed building when it is a benefit.
Regards,
Craig J. Gann, P.E.
www.EnergySimulators.com
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Amanda Bogner
Sent: Wednesday, February 27, 2008 8:45 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ASHRAE 90.1 & Shading from adjacent buildings
Can anyone confirm or refute that shading provided by adjacent buildings is
allowed to be included when modeling according to ASHRAE 90.1 PRM or ECB
protocol? I am not able to find any statements in the document related to
this specific issue.
If it is allowed, does it need to be provided on both proposed design and
baseline models? Or can it only be modeled on the proposed design like all
other shading devices?
Best Regards,
Amanda Bogner, PE LEED AP
404.806.2018 EXT 103
404.806.2019 FAX
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080227/34ca97c6/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/bmp
Size: 24894 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080227/34ca97c6/attachment-0001.bin>
More information about the Bldg-sim
mailing list