[Bldg-sim] FW:
Michael Tillou
michael.tillou at gmail.com
Fri Feb 22 09:52:32 PST 2008
The increase in heating energy is most likely the result of additional
boiler energy required to offset the reduced motor/pump heat being
transfered to the working fluid when you switched from a constant volume to
a variable volume pumping scheme.
Mike
Michael Tillou, PE, LEED
P: 413-458-9870 C: 413-652-1087
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Shruti
Kasarekar
Sent: Friday, February 22, 2008 12:09 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] FW:
Hello All,
I am modeling a 2 pipe FCU and when I change the 3 way valves to 2 way w/ a
VFD on Pump, I see a considerable increase in Space Heating. I checked that
the load on my coils is changing. Why? I did not change any other
parameters. Any ideas?
Thanks.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080222/32797d39/attachment-0002.htm>
More information about the Bldg-sim
mailing list