[Bldg-sim] FW: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baselinecase
Andrew Craig
andrew_c at ieice.com
Fri Jan 25 12:56:57 PST 2008
Mark---
The change occurred in addendum a to 90.1-2004. Here is the text:
Andrew Craig, EIT,LEED AP/ Mechanical Designer
INTERFACE ENGINEERING
direct 503.382.2696
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Zoeteman,
Mark R.
Sent: Friday, January 25, 2008 12:44 PM
To: Bldg-Sim
Subject: [Bldg-sim] FW: [BLDG-SIM] 90.1-2004 Appendix G Glazing for
Baselinecase
I've reviewed all the 90.1-2004 addenda and don't see where vertical
fenestration requirement of "distributing uniformly in horizontal bands
across the four orientations" has been removed. Addenda "as" which
refers to this section doesn't remove either.
Mark Zoeteman, FTC&H
-----Original Message-----
From: Zoeteman, Mark R.
Sent: Friday, January 25, 2008 3:40 PM
To: 'Michael.Rosenberg at state.or.us'; BLDG-SIM at gard.com
Subject: RE: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Michael
Rosenberg
Sent: Wednesday, May 16, 2007 1:47 PM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] 90.1-2004 Appendix G Glazing for Baseline case
The requirement to distribute fenestration uniformly in horizontal
bands across the four orientations has been removed from Appendix G in
the published Addenda Supplement to 90.1, 2004. See the ASHRAE website
for the supplement.
http://www.ashrae.org/technology/page/132
Michael Rosenberg
Oregon Department of Energy
625 Marion St. N.E.
Salem, OR 97301-3742
Phone : (503) 373-7809
Fax: (503) 373-7806
>>> Chris Jones <cj at cr-jay.ca> 5/16/2007 9:56:02 AM >>>
Appendix G notes that for the Baseline building: "Vertical fenestration
areas for new buildings and additions shall equal that in the proposed
design or 40% of gross above grade wall area, whichever is smaller, and
shall be distributed uniformly in horizontal bands across the four
orientations."
Does this mean that the Baseline building gets windows on all walls on
each orientation whether or not the Design case has a window in all
walls on each orientation. For example, if the west orientation has 30%
glazing overall but many spaces have no windows - some walls on the west
face have more that 30%. Do those spaces in the Baseline case get 30%
glazing? Or do I only put windows in the Baseline case where there are
windows in the Design case.
Thanks for any help!
Chris Jones, P.Eng.
14 Oneida Avenue
Toronto, ON M5J2E3
Tel. 416 203-7465
Fax. 416 946-1005
======================================================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed to the
BLDG-SIM at GARD.COM mailing list. To unsubscribe from this mailing list
send a blank message to BLDG-SIM-UNSUBSCRIBE at GARD.COM
_______________________________________________
Bldg-sim mailing list
Bldg-sim at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080125/b12381b2/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 40818 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080125/b12381b2/attachment-0001.jpeg>
More information about the Bldg-sim
mailing list