[Bldg-sim] Swimming pool modeling
Zarske, Jim
jzarske at nexant.com
Wed Jan 30 07:32:57 PST 2008
I cannot comment on Energy+. However, as far as eQUEST, I've modeled a
natatorium (indoor pool) including the latent load. In one of the
ASHRAE books, there's a methodology for determining the latent loads of
a pool as a function of activity, water temperature, and I believe a few
other factors. I ran through these calculations and inputted this load
into the "Internal Energy Sources" under the Equipment internal gains
tab. I created a schedule based on when the proposed pool cover would
be off (pool in use), and called it a "process" load. I believe I set
the Latent HG ratio to 1.0 and Sensible to 0.
The results of my model seemed to be reasonable.
Maybe with this methodology, it might allow you figure something out
with Energy+; otherwise, eQUEST may be your best, closest approximation,
for this project.
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dusko
Nikolic
Sent: Wednesday, January 30, 2008 2:20 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Swimming pool modeling
Hi,
Is it possible to model swimming pool in Energy+? I could not find the
way to model latent loads due to water evaporation
Thanks
Dusko Nikolic
Mechanical Building Services Engineer
MWH New Zealand Ltd DDI: (64-9) 580 4531
Level 2, Building C, Millennium Centre Fax: (64-9) 580 7600
600 Great South Road
PO Box 12-941, Penrose
Auckland, New Zealand
http://www.mwhglobal.com/nz <http://www.mwhglobal.com/nz>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080130/d419aa0e/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1683 bytes
Desc: ATT2298105.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080130/d419aa0e/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1160 bytes
Desc: ATT2298106.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080130/d419aa0e/attachment-0003.jpeg>
More information about the Bldg-sim
mailing list