[Bldg-sim] A question about ASHRAE baseline loop pump power
Howe, Timothy
Timothy.Howe at stantec.com
Tue Jun 17 05:55:34 PDT 2008
Set the mech efficiency then calc the required head needed as fred
stated.
Check out:
http://www.commercial.carrier.com/commercial/hvac/general/0,3055,CLI1_DI
V12_ETI10630,00.html#HAP49 for the calc.
Timothy Howe, MS, LEED(r) AP
Mechanical Engineer
Stantec
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Fred Porter
Sent: Tuesday, June 17, 2008 8:36 AM
To: bldg-sim at lists.onebuilding.org; yizhao1 at vt.edu
Subject: Re: [Bldg-sim] A question about ASHRAE baseline loop pump power
I deal with this by adjusting the "pipe-head" of the loop until the
total specific design pump power = 19 W/gpm, while still letting
eQuest/DOE2 "autosize" the pumps.
I believe this W/gpm should be calculated as (sum of all pump power for
both "primary" and "secondary" pumps connected to a loop)/design loop
flow. In addition to the loop (secondary) pump, the ASHRAE baseline
includes primary pumps, in DOE-speak, a "CHW-PUMP" and "CW-PUMP" for
each chiller, which is not the way eQuest sets things up by default. And
only the "primary" pump on the CW loop.
Fred
>>> <yizhao1 at vt.edu> 6/17/2008 12:10 AM >>>
Hi all -
I'm working on an ASHRAE baseline model with system #7 in eQuest. ASHRAE
requires the chilled water loop pump power of 19W/gpm. So I ran the
model with
the default head and pump kW (left then blank) first, and found the gpm
of the
pump from the report, then I calculated and input the kW of the pump.
However,
after I ran the model again with this pump power, the pump gpm result
was
changed in the report. Also, I got a warning that said the pump flow
input is
lower than the actual flow. There is no input for a pump flow. So I
don't know
what happened inside eQuest.
Do you know what is wrong here? How to model the ASHRAE loop pump power
correctly in eQuest?
Thanks a lot!
Ying
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080617/8782c229/attachment-0002.htm>
More information about the Bldg-sim
mailing list