[Bldg-sim] Modeling variable refrigerant flow system (VRF) in
Rosenberg, Michael I
michael.rosenberg at pnl.gov
Mon Jun 23 07:59:16 PDT 2008
Regarding the baseline system. If you are using Chapter 11 ECB, the
budget system would be System 8, Packaged Terminal Heat Pump if it is a
residential application and System 9, Packaged Rooftop Heat Pump if
non-residential. If you are using Appendix G, then the baseline system
depends on the building program per Table G.3.1.1A
Mike
Michael Rosenberg
Senior Commercial Buildings Energy Analyst
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Travis
English
Sent: Monday, June 23, 2008 7:44 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Modeling variable refrigerant flow system (VRF)
in
We've done some modeling of the VRF in EnergyPro.
The results are quite favorable, compared to traditional split systems.
Our understanding, as of last week, is that the module for modeling VRF
that is included in Trace is not endorsed by either of the major
manufacturers.
(Mitsubishi & Daikin) So, from their perspective, Energy Pro is
currently the ONLY way to model VRF.
We've had some internal debate as to what the corresponding 90.1
baseline system should be. I'd live to hear people's thoughts.
Travis R. English, P.E., LEED AP
Associate
TKSC
TSUCHIYAMA KAINO SUN & CARTER
Phone: (949) 756-0565
Mobile: (949) 735-6183
Email: <mailto:tenglish at tkscengineering.com>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Bldg-sim
mailing list