[Bldg-sim] Exceptional Calculation Method for Demand ControlledVentilation
Amanda Bogner
amanda at bvm-engineering.com
Tue Mar 18 09:28:14 PDT 2008
Unlike the experience that Aleka Pappas described, I have never been asked
by the USGBC to provide an Exception Calculation Method when using DCV in
eQuest. This only proves that the review process is not consistent...
Regardless, I've only modeled DCV using the minimum flow control options
under the Air-side HVAC tab within the thermal zones (MIN-FLOW-CTRL). You
have the option of DCV with reset up, reset up/down, or reset down.
If you're trying to model DCV in a different way, you probably should
provide documentation for an Exceptional Calculation Method. These are not
hard to put together. On the EAc1 template, there is a specific area that
you'll need to fill in - essentially describing the method you've used and
your reasons for it along with the energy and cost savings that method is
calculating. Read the instructions on the template - they're pretty
straightforward.
When I've done Exceptional Calculations Methods in the past, I've created a
new proposed case model as the USGBC will want to see output from the
proposed case model with the Exceptional Calcs and without it. You'll
document Table 1.8.2 on the EAc1 template with the data reported in the
proposed case model without the Exceptional Calculation Method.
Amanda Bogner, PE LEED AP
404.806.2018 EXT 103
404.806.2019 FAX
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jessica XP
Sent: Tuesday, March 18, 2008 10:13 AM
To: bldg-sim
Subject: [Bldg-sim] Exceptional Calculation Method for Demand
ControlledVentilation
Hi folks,
I am simulating a 24-floor building to be LEED certified. The software is
Equest. In order to achieve as many points as possible in EA CR1,
demand-controlled ventilation (DCV) has been modeled in the proposed design.
But we are not sure if this stragety needs Exception Calculation Method
requested by USGBC. In one of CIR historical archive of LEED online, USGBC
requested exceptional calculation method for schedule-based DCV models. I
have no idea if USGBC would treat DCV models in Equest as those of
schedule-based.
The use or removal of DCV will decisively impact the achieveable points of
EA CR1. I am wondering if anyone in this community has clear picture on this
issue.
Thanks in advance.
Jessi
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080318/29ae8c62/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/bmp
Size: 24894 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080318/29ae8c62/attachment-0001.bin>
More information about the Bldg-sim
mailing list