[Bldg-sim] Unmet loads.
Ümit Esiyok
umit.esiyok at uni-dortmund.de
Wed Mar 12 08:38:50 PDT 2008
Steve,
thank you very much indeed, yes you understood my question right. I was
just not sure because in the archiv of Bldg-sim I read that the results
can be found in BEPS and SS-F for each Zone.
> Umit-
>
> I'm not sure if I fully understand your question but I'll try to help you
> out. The number of hours that are not met can be found in the summary tab
> of the "Air-side HVAC" tab in eQuest. It's also listed in the .sim file,
> but its easily found within eQuest. The BEPS report does not give the
> number of hours, rather just the percentage. If your model is showing
> over
> 20% of the hours out of range you will definitely need to go back and
> resize
> your systems.
>
> --
> Steve Mignogna
> Atelier Ten
>
> On Wed, Mar 12, 2008 at 9:59 AM, Ümit Esiyok <umit.esiyok at uni-dortmund.de>
> wrote:
>
>> Dear all,
>>
>> my second question today. I would like to be sure if my understanding is
>> right or not about not met loads. Currently I am trying to fill up the
>> LEED EA Credit 1 submittal. Section 1.3 Advisory Messages There are :
>> 1. Number of hours heating loads not met
>> 2. Number of hours cooling loads not met
>>
>> I turn back to my e-Quest outputs ( BEPS Report) in the report I read:
>>
>> a. PERCENT OF HOURS ANY SYSTEM ZONE OUTSIDE OF THROTTLING RANGE
>> (Question:
>> this value is number of heating loads or should be written in LEED
>> submittal?)(20,9 for Proposed and 23,0 for Baseline, I am not mechanical
>> engineer but as much as I understood from ASHRAE number of hours not met
>> should not exceed 300)
>> b. PERCENT OF HOURS ANY PLANT LOAD NOT SATISFIED ( Question: this value
>> is
>> for both number of hours heating and cooling not met or just for
>> Cooling?)(Both in baseline and Proposed 0,0)
>>
>> regards
>>
>> --
>> Ümit Esiyok
>> Dr.-Ing., MSc. Arch.
>>
>> WS Greentechnologies
>> Stuttgart
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>
More information about the Bldg-sim
mailing list