[Bldg-sim] Shading projections-baseline building (LEED)
Kristin Field
KField at archenergy.com
Tue Mar 25 13:25:07 PDT 2008
Myrene,
You could consider any shading provided by the balconies as building self-shading, which isn't allowed in the Baseline and is allowed for the Proposed Design. Whether you call them shading projections or call their shading self-shading, I think they are not allowed in the Baseline and are in the Proposed. Let me know if anybody disagrees!
Kristin
>>> Myrene Giuliani <mygiuliani at yahoo.com> 3/25/2008 11:24 AM >>>
When constructing the baseline energy model, Appendix
G of ASHRAE 90.1 parameters specify that shading
projections are not to be included for the baseline
model. My question is, if the design of the building
includes balconies (it's a mid-rise residential
building) would they be considered shading
projections? My impression is that they are shading
projections, but I would like to confirm before
detailing the energy model.
Thank you,
Myrene Giuliani, LEED AP
____________________________________________________________________________________
Be a better friend, newshound, and
know-it-all with Yahoo! Mobile. Try it now. http://mobile.yahoo.com/;_ylt=Ahu06i62sR8HDtDypao8Wcj9tAcJ
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080325/931b27ba/attachment-0002.htm>
More information about the Bldg-sim
mailing list