[Bldg-sim] eQUEST - percent of hours outside throttling range
Vikram Sami
VSami at lasarchitect.com
Wed May 14 10:45:39 PDT 2008
Ramana,
Check your schedules - make sure you are ramping up (or down) your
temperatures in a reasonable increment. Also - make sure your fans are
allowed to turn on at the appropriate times too.
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com
Please don't print this email unless you really have to.
In the United States, we use enough office paper each year to build a
10-foot high wall that's 6,815 miles long or two and a half times the
distance from New York to Los Angeles.
~ Wisconsin Department of Natural Resources, "Recycling Facts and
Figures," PUBL CE-163, 2002.
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ramana Koti
Sent: Wednesday, May 14, 2008 12:13 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] eQUEST - percent of hours outside throttling range
Dear all,
I'm working on the energy model for a school building with 43 zones with
each zone connected to a ground source heat pump. Right now the model is
for design development but eventually the same model could be used for
LEED.
I can't seem to get the percent of hours any system zone outside of
throttling range below 48%. The system sizing ratio of all airside
systems is currently at 2. As per HVAC design, the depth of ground
source loop is 400 ft and I tried increasing it to 600 ft and that only
helps a little.
In the SS-R report, the undercooled hours for different zones are in the
200+ range while the underheated hours are in the range of 200 to 500.
I'm using the Dodge City, KS weather file.
Also the current annual energy consumption is as low as 18.1 kBtu/ft2, I
know that will change as the % hours outside the throttling range
changes but still seems very low.
Thanks for your help,
RAMANA KOTI Assoc. ASHRAE LEED(r) AP
Sustainable Building Analyst
ELEMENTS division of BNIM architects
106 West 14th Street Suite 200
Kansas City Missouri 64105
d 816.783.1635 f 816.783.1501
bnim.com | elements.bnim.com
-------------- next part --------------