[Bldg-sim] Appendix G Baseline System for un-air conditioned zoobuilding
Dan Katzenberger
dan at eeEnviro.com
Thu May 15 21:08:57 PDT 2008
Allan,
No. There are no requirements in ASHRAE 90.1-2004 Appendix G for cooling
space thermostat settings; therefore you are allowed to set the cooling
thermostat to any temperature that you choose as long as the settings are
the same for both the baseline and proposed models. You did not mention
whether or not your models are being used for LEED certification, but this
method of setting cooling thermostat setpoints high enough to eliminate
cooling energy has been accepted by USGBC Energy and Atmosphere TAG and LEED
reviewers on other LEED projects. Note that this is my personal opinion and
should not be taken as an official ruling from ASHRAE or USGBC.
Dan
Daniel A. Katzenberger, Principal, P.E., CEM, LEED-AP
Certified Energy Star Green Building Engineer
V.P. Minnesota Chapter of the Association of Energy Engineers
Voting Member USGBC Energy and Atmosphere Technical Advisory Group (EA TAG)
Engineering, Energy, and the Environment, LLC
"The Green Group"
420 North 5th Street, Suite 305, Minneapolis, MN 55401-1348
p. (612) 327-4210 f. (612) 338-5280
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Allan Fox
Sent: Thursday, May 15, 2008 2:48 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G Baseline System for un-air conditioned
zoobuilding
I am currently modeling a zoo building that is heated and ventilated only.
According to ASHRAE 90.1 Appendix G, I have to model both heating and air
conditioning even if no air conditioning exists. For this size building I
have to model a System 3 - rooftop air conditioner with gas heat for both
the base building and the proposed building. Is there anything in Appendix G
that would prevent me from setting the cooling thermostat setpoint up to 90
degrees to prevent cooling energy from being included in the simulation as
long as I use the same setting for both proposed and base models?
--
---------------------------
Allan Fox, P.E. CBCP, LEED AP
Senior Mechanical Engineer
afox at osborn-eng.com
OSBORN ENGINEERING
1300 East 9th Street Suite 1500 | Cleveland, OH 44114
t 216 861 2020 x3040 | f 216 861 3329 | osborn-eng.com
---------------------------
The information in this e-mail message, including any attachments, is for
the sole use of the intended recipient(s) as addressed, and may contain
confidential information. Any unauthorized review, use, copying,
disclosure, or distribution is prohibited. If you are not the intended
recipient, please contact the sender by reply e-mail and destroy all copies
of the original message. To view the complete email disclosure statement,
please visit our website at: http://www.osborn-eng.com/disclosure.html
C Copyright 2008 The Osborn Engineering Company. All rights reserved.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080515/31d0db5e/attachment-0002.htm>
More information about the Bldg-sim
mailing list