[Bldg-sim] eQuest 90.1 Window U Values
Amanda Bogner
amanda at bvm-engineering.com
Fri May 23 08:16:22 PDT 2008
Since the glazing needs to be modeled as an assembly, you also have to
verify the correct frame conductance is being used. This value is found in
the detailed edits under the window details.
Frame Conductance= 1 / [(1/u-value) - 0.197]
So, by example, if the ASHRAE 90.1 fenestration assembly u-value = 0.57, the
frame conductance should = 1/ [(1/0.57) - 0.197] = 0.642
When this is used in conjunction with the correct glass conductance (as
previously described), the output file will give the proper u-value averages
on the LV-D report.
Amanda Bogner, PE LEED AP
404.806.2018 EXT 103
404.806.2019 FAX
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill
Sent: Friday, May 23, 2008 9:11 AM
To: Aulbach, John; Josh Greenfield; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] eQuest 90.1 Window U Values
Will the glass-conductance conversion method give the "assembly" U-value? I
thought assembly U-value included the frame. Also, what would you do to get
the assembly SHGC?
Why not just pick an existing glass type code after finding one that most
closely matches the desired assembly U-value and assembly SHGC? I can
usually find one that is close to, if not exactly the same as, the required
values. The best match I see from the DOE glass library for U=0.57 and
SHGC=0.39 is GTC 6840 - Double Pilkington Arctic Blu/Air1/Clr6.
Select "Create another Glass Type Code" by right clicking on an existing
code in your component tree. Then "Load Component from Library" and pick
6840. Then change the properties of the affected glass types to reflect the
change in glass type code (above the glass type codes as listed in the
component tree).
William Bishop, EIT, LEEDR AP | Pathfinder Engineers LLP
Mechanical Engineer
3300 Monroe Ave., Suite 306
Rochester, NY 14618
TEL (585) 218-0730 Ext. 114
FAX (585) 218-0737
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please consider the environment before printing this email
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Aulbach, John
Sent: Thursday, May 22, 2008 7:34 PM
To: Josh Greenfield; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] eQuest 90.1 Window U Values
Under DOE2 Help, Dictionary/Glass-Type..
GLASS-CONDUCTANCE
The conductance of the glazing, excluding the outside air film coefficient.
The conductance given in glass manufacturers' data sheets usually includes
the outside air film resistance for a wind speed of 7.5 mph (summer) or 15
mph (winter). Table 10 <javascript:TL_5625.HHClick()> can be used to obtain
the corresponding value of GLASS-CONDUCTANCE. For example, if U(7.5 mph) =
0.64 Btu/ft2-hr-F, then GLASS-CONDUCTANCE = 0.79 (by interpolation). For
U-values of different glazing types, see manufacturers' data sheets or the
ASHRAE 1989 Handbook of Fundamentals, p. 27.16-17.
Table 10
Correspondence between Glass manufacturers U-value and GLASS-CONDUCTANCE
(excluding outside air film) [all values are in Btu/ft2-hr-F (W/m2-K)]
U-Value
(including outside air film)
GLASS CONDUCTANCE
(7.5 mph wind speed)
(15 mph wind speed)
0.1 (0.57)
0.10 (0.57)
0.10 (0.57)
0.2 (1.14)
0.21 (1.19)
0.21 (1.19)
0.3 (1.70)
0.33 (1.87)
0.32 (1.82)
0.4 (2.27)
0.45 (2.56)
0.43 (2.44)
0.5 (2.84)
0.59 (3.35)
0.55 (3.12)
0.6 (3.41)
0.73 (4.14)
0.68 (3.86)
0.7 (3.97)
0.89 (5.05)
0.81 (4.60)
0.8 (4.54)
1.05 (5.96)
0.95 (5.39)
0.9 (5.11)
1.23 (6.98)
1.09 (6.19)
1.0 (5.68)
1.43(8.12)
1.24 (7.04)
1.1 (6.25)
1.64 (9.31)
1.40 (7.95)
1.2 (6.81)
1.87 (10.62)
1.57 (8.91)
1.3 (7.38)
2.13 (12.09)
1.74 (9.88)
Josh:
Convert your GLASS-CONDUCTANCE to come up with the appropriate U-Value.
See the attached for an ASHRAE window I did.
Why didn't you start with the ASHRAE run as Base, rather than the Proposed
model first?
John R. Aulbach, PE, CEM
Project Manager
Nexant, Inc.
701 West Kimberly Ave., Suite 245
Placentia, CA 92870-6342 USA
Phone: 714-524-4402
Fax: 714-524-4407
email: jaulbach at nexant.com
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Josh Greenfield
Sent: Thursday, May 22, 2008 3:42 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] eQuest 90.1 Window U Values
I'm to the point in an Energy Model where I'm changing my 'Proposed Model'
to my 'Baseline Model' and I'm having issues changing the window data. For
the ASHRAE 90.1 region, the Assembly U value needs to be set to 0.57 and the
Assembly SHGC needs to be set to 0.39.where do I input these numbers?? The
only window data values eQuest is letting me change is Glass Conductance,
VLT and Emissivity.
Josh Greenfield, PE, LEED AP
Senior Associate
Primera Engineers, Ltd.
100 S. Wacker Drive, Suite 700
Chicago, IL 60606
312.606.0910 Main
312.242.6392 Direct
312.606.0415 Fax
<blocked::mailto:jgreenfield at primerachicago.com>
jgreenfield at primerachicago.com
<http://www.primerachicago.com> http://www.primerachicago.com
Be Green...please consider the environment before printing this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080523/66e0981c/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/bmp
Size: 24894 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20080523/66e0981c/attachment-0002.bin>
More information about the Bldg-sim
mailing list