[Bldg-sim] ERV with increasing cooling load
Kingsley, Michael L.
MICHAEL.L.KINGSLEY at saic.com
Tue Oct 28 05:09:01 PDT 2008
Shaojie,
Check to make sure that you are not recovering heat during hours that
you can be using the economizer. Choose the Control Sequences:
Operation: "When Minimum OA" so that the heat recovery device will only
operate when you cannot benefit from free cooling.
Mike
Michael L. Kingsley, PhD, PE, LEED AP
Senior Engineer/ Project Manager
SAIC
6390 Fly Road
East Syracuse, New York 13057
Phone: (315) 437-1869 x205
Cell: (315) 373-4081
Fax: (315) 437-1866
Email: kingsleym at saic.com
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of eric wang
Sent: Monday, October 27, 2008 11:32 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] ERV with increasing cooling load
Hi,
I model a PSZ system with exhaust air heat recovery. I set the static
pressures of supply/exhaust fans as zero in ERV tab. Therefore, the fan
energy is the same with or without ERV. However, there is an increasing
cooling load in the cooling model. I changed the hourly report and
didn't find the reason. Any suggestions are highly appreciated.
Thanks
Shaojie