Why wouldn't you want the max to be 100% to take advantage of economizer
free-cooling if the climate and system configuration allowed for it. I
agree that there are large energy implications of conditioning excessive
OA and there may be viable means to limit it when you don't need it, but
there are also large implications of cooling return air when you don't
have to. Considering ASHRAE 90.1 mandates economizers under certain
climates, you would be penalizing yourself by capping OA.
Any thoughts?
Luka Matutinovic
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Doebber,
Ian
Sent: Monday, September 01, 2008 3:55 PM
To: bldg-sim at lists.onebuilding.org
Cc: Doebber, Ian
Subject: [Bldg-sim] Minimum OA Ratio for VAV System
ASHRAE 90.1-2004 does not specifically state anywhere a MAXIMUM OA RATIO
that a VAV system can not exceed. Yet ASHRAE 62-2004 insinuates this
with its reference to Ventilation Effectiveness based on OA Ratio (Zp)
in Table 6-3.
It would make perfect sense that a VAV system should be limited to never
have an OA Ratio exceed say 0.45. This is applicable especially in
heating where the effects of Thermal Stratification will cause
Ventilation Short Circuiting.
VAV control systems have the capability of limiting the OA Ratio which
has extremely large Energy Implications. For example, if the MAXIMUM OA
RATIO is 0.45, then the VAV system is limited to the how low the Total
Supply Air can reduce to. Consequently a lot more fan energy will be
required to maintain that higher Flow Rate.
Has anyone ever incorporated a MAXIMUM OA RATIO in their VAV System
Design?
Regards,
Ian Doebber