[Bldg-sim] District Thermal System
Eric Youngson
ericy at pae-engineers.com
Tue Sep 9 10:07:53 PDT 2008
Thanks Paul,
I guess I was just stating that the comparisons on equipment are
not so direct when you have one source from a DES system. Also, I'm not
really sure if I'm interpreting correctly that the DES being modeled in
the proposed but not in the baseline is fitting the intent of holding
the upstream equipment cost neutral. I suppose that it is as long as the
heating source is separately metered and the rate applied is the same.
Thanks,
Eric
-----Original Message-----
From: Paul Riemer [mailto:Paul.Riemer at dunhameng.com]
Sent: Tuesday, September 09, 2008 9:55 AM
To: Eric Youngson
Subject: RE: Re: [Bldg-sim] District Thermal System
Eric,
You stated you were using campus steam but I don't quite follow the last
paragraph or what you are doing on cooling.
If you are installing a chiller in & for your building, yes the tables
G3.1.1A & B stand and you might have chiller versus DX in both Step 1
and Step 2.
If you are using campus chilled water then step 1 has both models with
purchased chilled water and step 2 has your campus system versus the
Table G3.1.1A & B system.
There is an ASHRAE 90.1 addenda that you can elect to follow that
changes the crossover points for Table G3.1.1A. You may want to track
that down but I would guess it might save you some effort at the cost of
reduced savings.
I agree the new document generally makes it harder to show the 14%
savings.
Good luck,
Paul
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Eric
Youngson
Sent: Tuesday, September 09, 2008 11:40 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] District Thermal System
Sim List,
I'm simulating a LEED DES model of a campus central steam plant.
Under the new requirements discussed below specifically addressing 'step
1'. The way that I read the document, step 1 requires that the "upstream
equipment [be] modeled as COST neutral" (Table 1, p.4) while the
baseline DES system is compared with a proposed system "As Designed"
(Table 3, p.6) which suggests that the upstream DES equipment (including
its inefficiencies) shall be modeled in the proposed building for step
1.
If I am reading this correctly, it would be much more difficult
to acquire the required 2 points for certification (14% - NC) than
previously suggested.
Also, the comparison for systems not directly affected by the
DES central plant (chiller in my case) is not necessarily a direct
comparison. My building is ~75,000 SF & 3 floors (fossil fuel /
purchased heat), therefore according to Table G3.1.1A & B my baseline is
system 5 Packaged VAV w/Reheat - cooling type: direct expansion.
Any and all thoughts on this topic are welcome
Thanks
Eric
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of David S
Eldridge
Sent: Thursday, August 07, 2008 9:02 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] District Thermal System
It seems that the intention here is that if a credit is taken for an
exemplary LEED building for energy efficiency, it will have to overcome
district energy system (DES) inefficiencies if they are present. But at
the same time, you are able to get the minimum two EAC1 credits, to some
degree regardless of how bad the DES performs - so not excluding most
projects, but limiting the options for those projects with inefficient
infrastructures. This recognizes some of the constraints that a campus
project might encounter.
Likewise an efficient DES that may have efficient equipment,
cogeneration, heat recovery or other efficiencies will benefit the LEED
project and the team is rewarded for having built onto this type of
system.
Step 1: Building stand-alone scenario - for EAP2 compliance as well as
documenting up to two EAC1 credits. In both cases will be purchased
from district energy systems for heating and cooling as appropriate.
This I think was the discrepancy between Fred and Julia's posts - the
USGBC document states on page 8 that the actual prices are to be used,
so it would include the overhead and profit components for a commercial
DES. For campus situations without a "price" you must calculate the
equivalent value and it isn't specified if this includes the overhead
components.
If your building used DES for only one source, then the other source
would be modeled as proposed with the baseline equipment per App G.
So as Fred mentioned, it will be DES vs DES, chiller vs chiller, or
boiler vs boiler, etc.
If only pursuing EAP2 and two or fewer EAC1 credits (and achieving
them?), stop here.
Step 2: Aggregate building - for pursuit of additional EAC1 credits -
here the DES will be modeled for electricity and fuel usage, and
compared to a building with baseline heating and cooling equipment per
App G.
The key point of the text is "virtual on-site equipment representing
upstream" systems. So not exactly that system, but representing the
LEED project's share of that system.
Putting some numbers to a cooling plant for example purposes, the
intention is not for you to model a 500 ton load building being served
by a plant with four 5,000 ton chillers. Neither is the intention that
you should model the other buildings making up the 19,500 ton
difference.
The simulation programs are generally able to use efficiency
calculations based on the total plant, but imposed on a theoretical
smaller "virtual" plant serving the load of the new project. This is a
reasonable approximation to the share of the plant energy for the new
project assuming the cooling/heating loads are following the profile of
the DES in general. The virtual 500 ton chiller will have capacity
specified to match the LEED project's demand, but with the efficiency
curves and EIR of the existing 5,000 ton chillers.
Obviously the capacity of everything in the plant would have to be
adjusted, not just the chillers and boilers - include pumps, cooling
towers, etc.
There is a statement about Step 2 only providing up to four additional
EAC1 credits over Step 1, up to a maximum total of ten credits (like
normal). But my interpretation of the document is that even if you
documented six EAC1 credits in step 1, you can only claim two of them
unless you unlocked that potential by proceeding to Step 2. Is this
everyone else's interpretation also?
Hope this helps!
David
> -----Original Message-----
> From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-
> bounces at lists.onebuilding.org] On Behalf Of Craig Simmons
> Sent: Thursday, August 07, 2008 8:47 AM
> To: bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] District Thermal System
>
> Hi May,
>
> I interpret the update differently. It does not state that the
capacity
> must
> be the same, only that the efficiencies must be the same. I believe it
is
> expected that you create a virtual onsite plant sized to replace the
loads
> normally covered by the DES. The virtual plant must have the same
> efficiencies as the actual plant, but not the same capacity. In
addition
> you must implement a calculation or approximation to account for
losses in
> the distribution system. I believe that the statement "the DES central
> plant
> itself shall always be modeled as a total, entire unit" is to prevent
the
> model from combining the virtual plant (to cover DES loads) with any
> supplementary onsite plants that may exist. I don't think it is
intended
> that you model the DES at its actual capacity.
>
> Anyone else have a different opinion?
>
> Craig Simmons
>
> The Green Engineer, LLP
> Sustainable Design Consulting
> 50 Beharrell Street
> Concord, MA 01742
> t: 978/369-8978
> craig at greenengineer.com
> www.greenengineer.com
>
> Please consider the environment before printing this email. Thank you.
>
>
>
> -----Original Message-----
> From: May Xu [mailto:may.xu at hok.com]
> Sent: Tuesday, August 05, 2008 10:20 PM
> To: Jeff Haberl; bldg-sim at lists.onebuilding.org
> Subject: Re: [Bldg-sim] District Thermal System
>
> Hi Jeff,
>
> Thanks, I found many useful information there, it is a very good
> resource! However, I didn't get relative answers regarding my
question,
> which is about the simulation rule updated by USGBC recently about the
> district thermal system. Could anyone give me any suggestions?
>
> Thanks a lot!
>
> May
>
> -----Original Message-----
> From: Jeff Haberl [mailto:jeffhaberl at tees.tamus.edu]
> Sent: Tuesday, August 05, 2008 11:36 AM
> To: May Xu; bldg-sim at lists.onebuilding.org
> Subject: RE: [Bldg-sim] District Thermal System
>
> May:
>
> The Laboratory has spent quite a bit of time modeling the thermal
plant
> on the Texas A&M Campus with good success. Unfortunately, we ended up
> using some rather complex, interacting loop models with chiller
on/off,
> staging algorithms, etc.
>
> We have a number of papers and thesis on this at our web site
> "www-esl.tamu.edu" look under publications.
>
> Jeff
>
> 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) :=') 8=) 8=) 8=?
> Jeff S. Haberl, Ph.D.,
> P.E.............................jhaberl at esl.tamu.edu
> Professor......................................................Office
> Ph: 979-845-6507
> Department of Architecture.......................Lab Ph: 979-845-6065
> Energy Systems Laboratory.......................FAX: 979-862-2457
> Texas A&M University..............................77843-3581
> College Station, Texas, USA.......................URL:
www-esl.tamu.edu
> 8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) 8=? 8=) 8=) 8=)
>
> ________________________________
>
> From: bldg-sim-bounces at lists.onebuilding.org on behalf of May Xu
> Sent: Mon 8/4/2008 4:53 AM
> To: bldg-sim at lists.onebuilding.org
> Subject: [Bldg-sim] District Thermal System
>
>
>
> Dear All,
>
>
>
> I'm now working on a project using Districted Heating System provided
by
> a municipal system. The municipal system is working for a very large
> areas providing steam for about hundred buildings. And my building is
> one of them.
>
>
>
> According to the latest update issued by USGBC
> (https://www.usgbc.org/ShowFile.aspx?DocumentID=4176), the modeling
will
> be implemented by two steps. My question is about Step-2 (Aggregate
> Building/DES Scenario). In step-2, the energy source of Proposed
> Building is virtual on-site chiller representing upstream DC system.
The
> document also issues "The DES central plant itself shall always be
> modeled as a total, entire unit." My understanding is that it requires
> to model the central plant with the full capacity that is able to
> provide heating for all of buildings in whole district. However, if
> doing so, the energy consumption of the proposed building may be quite
> quite high, since it includes the energy consumption of the whole
> heating plant!! But my building is only one of the 100 buildings that
> are heated by the central plant. It is weird and I don't think it is
> what USGBC asked for. Does anyone know what shall I do for the
proposed
> building in Step-2?
>
>
>
> Thank you.
>
> May Xu, LEED(r)AP
> Project Engineer - Sustainable Design
>
> HOK
> Suite 3705A, Ciro` s Plaza,
> 388 Nan Jing West Road,
> Shanghai, 200003, PRC
>
> Tel: (86 21) 6334.6181 ext. 2230
> Fax: (86 21) 6334.6182
>
>
>
> www.hok.com <http://www.hok.com/>
> www.hokasiapacific.com <http://www.hokasiapacific.com/>
>
> Please consider the environment when printing this email.
> This email message is for the sole use of the intended recipient(s)
and
> may contain proprietary and/or confidential information. Any
> unauthorized review, use, disclosure or distribution is prohibited.
If
> you are not the intended recipient, please contact the sender by reply
> email and destroy all copies of the original message. Thank you .
>
>
>
>
>
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
BLDG-SIM-
> UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Bldg-sim
mailing list