[Bldg-sim] CFD Software for Built Environment
Paul Carey
Paul at zed-uk.com
Thu Sep 11 09:06:17 PDT 2008
Daniel
I'm a gambit fan, nice and easy to use and means you are in control of what
is going on with the grid, though have to say that I've used Pointwise
recently and find that is quicker as a pre-processor, but obviously an
additional cost.
I rather like those test papers you gave links too. My research work is
referenced throughout it...lol. Had a feeling it might have been though
seeing the person was working my own PhD supervisor.
Regards
Paul
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Costola, D.
Sent: 11 September 2008 16:51
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] CFD Software for Built Environment
Hi Claire and Paul,
Regarding CFX versus Fluent, my experience is that the "standard" pre
processing tools are quite different.
Gambit, the standard pre-processing tool for Fluent, is as user-friendly and
powerful as CFX-Ansys.
Just one example:
On CFX (even the old CFX-Build) is relatively simple to create unstructured
meshes with good control and, very important, the prism layer in the solid
boundaries. I couldn't produce the same meshes using Gambit.
Other important difference is the simulation automation process.
On CFX the variables have meaningful names, and a lot of things can be done
using simple text files and the graphic interface. On Fluent you need to
compile small programs with complex syntax even for routine tasks such as
create an inlet profile.
Finally, no matter the program you use, spend some time reproducing
benchmark results to assure that you have mastered the program.
My experience is mainly in outdoor simulation, where you have some nice
guidelines and benchmark data:
http://www.costc14.bham.ac.uk/documents/Wg2/FinalDocument.pdf
http://www.mi.uni-hamburg.de/fileadmin/files/forschung/techmet/cost/cost_732
/pdf/BestPractiseGuideline_1-5-2007-www.pdf
http://etheses.nottingham.ac.uk/archive/00000091/01/TongYangThesis2004.pdf
About the benchmark data/cases for indoor flow I don't know.
Regards
Daniel Cóstola
TU/e
Department of Architecture, Building and Planning Den Dolech 2 - Vertigo
6.16 - P.O Box 513 - 5600 MB Eindhoven - The Netherlands Phone +31 40 247
5760 Fax +31 40 243 8595 d.costola at tue.nl
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Paul Carey
Sent: donderdag 11 september 2008 16:02
To: 'Claire Das Bhaumik'
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] CFD Software for Built Environment
Claire,
Not a great deal of difference as far as I know. My friend at Buro Happold
uses CFX instead of Fluent without any problems on the work he does. It's
possibly more tightly integrated than Fluent in ICEM or AI workbench at a
guess as they've had it longer. As far as I know it's also cheaper and
thats got to be a good aspect as if it can do more or less the same for less
money I know which I'd be getting. There are probably differences in the
turbulence models available, etc but without looking into a detailed
breakdown of features I can't really help there.
Regards
Paul
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Claire Das
Bhaumik
Sent: 11 September 2008 09:48
To: Paul Carey
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] CFD Software for Built Environment
Any idea about ANSYS CFX?
ANSYS own both codes now and tell me that CFX can do everything that Fluent
can do and recommended it to me really in preference to Fluent for building
applications. What's the difference?
Thanks,
Claire
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Paul Carey
Sent: 10 September 2008 15:25
To: 'antixs antixs'
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] CFD Software for Built Environment
Antixs, et al
Airpak is okay and is perfectly adapted to HVAC applications as it includes
fan details, etc allowing you introduce swirl, etc. It is expensive for
what you get though. It has improved, but the gridding was fairly rough and
ready if you get complex geometry and can throw a wobbly if you are doing
external flow analysis for things like pedestrian comfort assessments where
you could need large variance in your grid cell size. If you are doing
rooms, etc you'll be fine. I'd agree with Kai's comments though.
Not used FloVent. It's quite pretty from memory, it's outputs are well
suited to HVAC work and make the whole CFD (Colour For Directors) stand up.
Whether it is good for complex analysis I'm not sure and will have to leave
that to others to comment on.
CHAM's flair is HVAC specific and there is even a link with Hevacomp so if
you've done your room calculations in that then there is a reduced version
which will let you do some basic flow analysis.
The problem with most of these simplified tools however tends to be the
gridding which has a tendancy to let them down and so convergence of
solutions can be hard to achieve. It really does depend on what you are
going to use it for and what sort of problems.
Sorry about copying your message below to the list Kai, but I think others
will lose the thinking of the thread and my comments as well, hope you don't
mind.
Cheers
Paul
From: Kang, Kai [mailto:Kai.Kang at jacobs.com]
Sent: 10 September 2008 14:52
To: antixs antixs; Paul Carey
Subject: RE: [Bldg-sim] CFD Software for Built Environment
Antixs,
Both Airpak and Flovent are customized CFD programs for building HVAC
applications. Airpak wraps around the basic Fluent solver, and provides a
user-interface that is much more geared towards building engineers, as well
as some additional functions that is only available with Airpak, such as
solar heat gain.
I have some experience with Airpak a while ago, being a Fluent user for many
years, I did not find any problem of learning the program and will say an
engineer without prior experience should be able to pick up the modeling
pretty quickly - the problem, however, is that if there is any issue with
the model, such as if the solution is diverging, it is very difficult to
"debug" the model in Airpak. I assume the same would be for Flovent, so in
essence I would say they provide the easiness in "cookie-cutter"
applications.
I am not copying this to the entire mailing list, as I may be talking a bit
too specific.
Regards,
Kai
________________________________
From: antixs antixs [mailto:antixs.antixs at gmail.com]
Sent: 10 September 2008 14:36
To: Paul Carey
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] CFD Software for Built Environment
Paul,
Thanks for such detailed information! They are really helpful. Do you have
any experience with Airpak and Flovent? Heard that these two tools are
specially tailored for built environment.
Thanks again.
antixs
On Wed, Sep 10, 2008 at 4:39 PM, Paul Carey <Paul at zed-uk.com> wrote:
Antixs
I think this depends largely on your budget and proficiency.
If you want to go full on with CFD, then I'd suggest Fluent
(http://www.fluent.com/) everyday. It is very widely used and well trusted
tool. ICEM is a good meshing tool, but we like Pointwise and Gridgen for
it's meshing simplicity.
Other than that, I know CCM+ from CD-Adapco (http://www.cd-adapco.com/) is
very good too. Makes the job quite easy. These tools are very expensive
though.
If you want the same sort of capability and are willing to use mainly text
input then I'd suggest OpenFoam (http://www.openfoam.org) - a very powerful
open source CFD tool. You could use something like pointwise to mesh it,
output a fluent case file and then openfoam has it's own fluent case file
converter program which you could use to then convert it and process it.
You'd probably need a decent post processor too, but clearly then you are
only paying for those programs as openfoam itself
is free. If you can do it all by text then you wouldn't need to pay
anything at all. It will require you to use Linux though. I saw a
pre-compiled bootable live CD distro of this recently which was quite
impressive so it allows you to check it out just by inserting CD into
computer and booting to it. The link for that is:
http://www.caelinux.com/CMS/
Of the cheaper and possibly more usable programs for quick built environment
analysis. Cham Pheonics (http://www.cham.co.uk/) is good value for money.
It's Flair add on is pretty simple to use. I'd still personally get a good
CAD program to make sure your geometry is spot on before importing it, but
then it would do the job well. A lot of companies use it becasue of it's
relative simplicity and good price.
Another which is aimed at non-CFD experts is DesignBuilder CFD
(http://www.designbuilder.co.uk/). It is in beta test stage and looks
promising. It'll be great for simple stuff. Wouln't recommend anything
that uses just cartesian grids for complex jobs, but for the large majority
of jobs it will suit, especially if it's internal room flows, etc. Should
be quite competitive on the price too.
Hope that helps.
Regards
Paul
Dr Paul Carey
Director
Zero Energy Design Ltd
10A Portland Place
2-22 Mottram Road
Stalybridge
SK15 3AD
UK
T: +44 0161 3386200
F: +44 0161 3031281
M: +44 0789 4098012
E: paul at zed-uk.com
http://www.zed-uk.com/
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of antixs antixs
Sent: 10 September 2008 05:13
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] CFD Software for Built Environment
Hi all,
Just wonder what CFD softwares are popularly used for analyzing built
environemnt in architect/MEP consulting firms? Also which one is relatively
eaiser to use?
Many thanks.
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.169 / Virus Database: 270.6.19/1661 - Release Date:
9/10/2008 6:00 AM
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.169 / Virus Database: 270.6.19/1664 - Release Date:
9/10/2008 6:00 AM
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The service is powered
by MessageLabs. For more information on a proactive anti-virus service
working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The service is powered
by MessageLabs. For more information on a proactive anti-virus service
working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________
________________________________
This message (and any associated files) is intended only for the use of the
individual or entity to which it is addressed and may contain information
that is confidential, subject to copyright or constitutes a trade secret. If
you are not the intended recipient you are hereby notified that any
dissemination, copying or distribution of this message, or files associated
with this message, is strictly prohibited.
If you have received this message in error, please notify us immediately by
replying to the message and deleting it from your computer. Messages sent to
and from us may be monitored.
Internet communications cannot be guaranteed to be secure or error-free as
information could be intercepted, corrupted, lost, destroyed, arrive late or
incomplete, or contain viruses. Therefore, we do not accept responsibility
for any errors or omissions that are present in this message, or any
attachment, that have arisen as a result of e-mail transmission. If
verification is required, please request a hard-copy version. Any views or
opinions presented are solely those of the author and do not necessarily
represent those of the company.
The ultimate parent company of Scott Wilson Group is Scott Wilson Group plc.
Registered in England No. 5639381
Registered Office: Scott House, Alençon Link, Basingstoke, Hampshire
RG21 7PP
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.169 / Virus Database: 270.6.19/1665 - Release Date: 9/11/2008
7:03 AM
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
No virus found in this incoming message.
Checked by AVG - http://www.avg.com
Version: 8.0.169 / Virus Database: 270.6.19/1665 - Release Date: 9/11/2008
7:03 AM
More information about the Bldg-sim
mailing list