[Bldg-sim] Thermal Storage Controls
    Alan Jackson 
    Alan.Jackson at BuroHappold.com
       
    Tue Aug 11 07:55:40 PDT 2009
    
    
  
Eric
 
That did the trick. Thanks for the help. And it seems I had to introduce
different controls then I was at the time in order to get the storage
tank to provide capacity to the loop at the appropriate time. For
others, this is detailed in STORE-MAX-LOAD of DOE documentation. Example
below.
 
CHILLERS-1                  = (CHLR-A,CHLR-B)
CHILLERS-SEQ-1          = (     1,     2) 
STORE-SEQ-1               = (3)
 
Thanks again
 
Alan Jackson, LEED(r) A.P. 
Senior Mechanical Engineer
Buro Happold Consulting Engineers, PC
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Eric Studer
Sent: Tuesday, August 11, 2009 6:37 AM
To: Alan Jackson; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Thermal Storage Controls
 
I get that error when I do novel things, too, and it goes away when I
change the loop sizing type from secondary (the default) to primary.
You may get a warning afterwards that says that the loop is undersized
for the connected load.  I ignore these warnings since the loop is sized
based on the primary equipment capacity (which should be sufficient).
 
I hope this is helpful!
 
Eric
 
Ph:   (781) 431-1100 ext 12
Fax:  (781) 431-1109
 
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Alan
Jackson
Sent: Monday, August 10, 2009 4:53 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Thermal Storage Controls
 
I am modelling the cost benefits of creating chilled water/ice at night
so I have added a thermal storage tank and set up a secondary chiller
and loop to serve the storage tank. I have assigned an on/off schedule
to the TES chiller so that it operates only at night, but I have also
added equipment controls so that it has first priority for cooling. This
was my initial thought on getting it to operate at night but not during
the day. I am getting an error "Ice Water Loop has zero design flow". At
first I figured this was because I had no size for the storage tank
selected so I started off small and through a 50 ton tank in the
capacity field. Still receiving the same error. Does this have to be
sized manually?
 
Here are the controls:
 
"Chiller Controls" = EQUIP-CTRL      
   TYPE             = COOLING
   CIRCULATION-LOOP = "Chilled Water Loop"
   CHILLERS-1       = ( "Ice Chiller" )
   CHILLERS-2       = ( "Air Cooled Chiller 1" )
   ..
 
and the tank
 
"Ice Storage" = THERMAL-STORAGE 
   TYPE             = COLD-WATER-TANK
   CAPACITY         = 600
   CHRG-LOOP        = "Ice Water Loop"
   CHRG-SCH         = "Ice Making Schedule Annual"
   DCHRG-LOOP       = "Chilled Water Loop"
   ..
 
 
 
Thanks in advance
 
 
 
Alan Jackson, LEED(r) A.P. 
Senior Mechanical Engineer
Buro Happold Consulting Engineers, PC
100 Broadway 
New York, NY 10005
USA
 
Tel: (+1) 212 334 2025
Direct: (+1) 212 616 0267
Fax: (+1) 212 334 5528
Email: alan.jackson at burohappold.com
www.burohappold.com <http://www.burohappold.com/> 
 
This transmission is confidential and intended solely for the person or
organization to whom it is correctly addressed. If you are not the
intended recipient of this transmission, you should not take any action
in reliance on it. Further, this transmission may contain confidential
design and other information owned by Buro Happold Consulting Engineers
PC. You should not copy, distribute, use, offer for sale or hire such
information or in any way infringe the design and intellectual property
rights of Buro Happold Consulting Engineers PC. It is intended that
communication by email from Buro Happold Consulting Engineers PC or its
employees is limited to communications connected to the services
provided by Buro Happold Consulting Engineers PC. Buro Happold
Consulting Engineers PC accepts no liability for any communications not
connected to the services it provides. Computer viruses may be
transmitted or downloaded onto your computer system via email
communication. It is the recipient's responsibility to take any action
necessary to prevent computer viruses being transmitted in this way.
Accordingly, Buro Happold Consulting Engineers PC disclaims all
responsibility which arises directly or indirectly from such
transmission of computer viruses.
 
 
This message has been scanned by MailController
<http://www.mailcontroller.altohiway.com/> .
 
This message has been scanned by MailController
<http://www.mailcontroller.altohiway.com/> .
Click here
<https://www.mailcontroller.altohiway.com/sr/XDghBku0TL3TndxI!oX7Urq5v!b
vD4NVF8LwKcnmBTJO5anMW+F70E5rZtJ!paq1qcOGoLX7V4E5ky06sDJQ0Q==>  to
report this email as spam.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090811/f801c99d/attachment-0002.htm>
    
    
More information about the Bldg-sim
mailing list