[Bldg-sim] Variable Speed Screw Chiller Curves
Dan Russell
danr at engineeringinc.com
Wed Dec 2 08:35:15 PST 2009
Well, I’m going over a year back into the archives, but hopefully someone can help. I’m modeling a project with 500 Ton Carrier Evergreen Water-Cooled Screw Chillers and would like to take advantage of the part-load efficiency benefits. It appears that Dan Nall posted custom efficiency curves for this specific equipment a while back, but when I use them in eQUEST my cooling energy gets tripled (from 800 MWh to 2450 MWh) as compared to the default eQUEST curves for Water-cooled Screw chillers. Does anyone have experience using these curves effectively? Am I misinterpreting the curve data? Are they intended for something other than eQUEST inputs? Or are the default eQUEST curves unrealistically efficient?
Thanks for any input,
Dan Russell
Engineering Incorporated
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Dan Nall
Sent: Tuesday, August 26, 2008 1:17 PM
To: Kingsley,Michael L.; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Variable Speed Screw Chiller Curves
Try these on for size;
"VFDSCrew EIR fPLR" = CURVE-FIT
TYPE = CUBIC
INPUT-TYPE = DATA
INDEPENDENT = ( 1, 0.75, 0.5, 0.25 )
DEPENDENT = ( 1, 0.97307, 1.01436, 1.3616 )
..
"Carrier-EIR-fCHWT&CWT" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( 0.767051, -0.0236208, 0.0004375, 0.0024939, 0.0002337,
-0.000418 )
..
"Carrier-EIR-fPLR&dT" = CURVE-FIT
TYPE = BI-QUADRATIC-RATIO&DT
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( -0.0230025, 0.902964, 0.0935993, 0.00347819,
-2.45759e-005, -0.00196462 )
..
"Carrier-CAP-fCHWT&CWT" = CURVE-FIT
TYPE = BI-QUADRATIC-T
INPUT-TYPE = COEFFICIENTS
COEFFICIENTS = ( 0.448509, 0.0185587, -0.00028125, 0.00306901,
-5.0201e-005, 0.000108475 )
-----Original Message-----
From: "Kingsley, Michael L."
Sent: Aug 26, 2008 2:15 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Variable Speed Screw Chiller Curves
Does anyone have DOE-2 performance curves for a variable speed screw chiller (I believe the Carrier Evergreen 23XRV is the only one now) that they would be willing to share?
Thanks in advance.
Michael Kingsley