[Bldg-sim] IES-VE Energy
Karen Walkerman
kwalkerman at gmail.com
Thu Feb 26 11:16:51 PST 2009
Carol said most of it, and I definitely second the prohibitive cost for a
program like IES-VE for a small shop, but I've used Trace700, which I assume
uses an iterative algorithm (it took about 1-2 hours run-time). So maybe
using an iterative algorithm gives a little more accuracy, I'd guess on the
order of 2-5%, BUT many of these programs don't allow you the flexibility in
your inputs to take advantage of the iterative nature of the program. For
many systems, you don't need to use an iterative program, you just need to
know the hourly space loads, hourly ventilation loads, and equipment
operation efficiencies at the given conditions. You need just a few layers:
component load (walls, windows, internal loads, etc), zone loads, hvac
system loads, loop loads and plant loads, in order to get pretty good
results. You need a few additional levels when your systems get more
compliated, but it doesn't require a super-complicated algorithm.
Bottom line is, many programs have their drawbacks. eQuest is not good at
modeling natural ventilation, precisely because it is not a CFD program. If
it were good at modeling natural ventilation, it wouldn't be able to run in
1-2 minutes.
I'd love to see a program that could integrate into two simulation engines,
one quick engine for trouble-shooting, doing DD models and running lots of
alternatives, and then an interative simulation engine for more complex
stuff, natural ventilation, complicated HVAC system configurations, etc.
Add that one to the wish-list! Maybe we'll see it in 20 years.
--
Karen
On 2/26/09, Carol Gardner <gems at spiritone.com> wrote:
>
> It can be better because you only have to do the renaming process once and
> then your done whereas you are going to have to do the rerunning way more
> than once: at least 4 orientation runs, a run for each energy efficiency
> measure, a run each time you realize you forgot to do the ____(fill it in).
> You are way further ahead using eQUEST. I'm not sure what you mean by an
> interactive 3D viewer, I find eQUEST's 3D views really helpful but I get the
> impression you are talking about something else. At any rate, I have used
> IESVE and E+ and I think they both excel in ways that eQUEST doesn't but
> IESVE is just too expensive for a single shop person like me and E+ is just
> too slow so far. I don't rule them out for use when I'm rich and they're
> faster, though.
>
> Carol
>
> Paul Carey wrote:
>
>>
>> Karen and all,
>>
>> I’m confused here....how can a program that takes up to 3 hours to rename
>> the zones but then takes minutes to get results, be better than something
>> that takes a few minutes to rename, but then takes a couple of hours to run?
>> They are about the same surely? The only advantage I can see is that further
>> iteration might be quicker in the former assuming your geometry doesn’t
>> change.
>>
>> I have been using various modelling tools such as IES VE, TAS and
>> DesignBuilder as well as a few other tools when necessary (Fluent & CHAM CFD
>> etc) since the late 90s. IES is good, it’s quick to produce models and
>> excellent for dynamic natural ventilation design. TAS is better at the HVAC
>> and natural ventilation design aspects than IES and I think it’s more
>> accurate, but it’s front end still lacks some of the functionality of other
>> tools. Hopefully that is being addressed by their links with Bentley. My
>> colleague, Chris Yates (also on this list) has become a bit of a wiz with
>> the sketchup plug in for IES and this appears to be much better than relying
>> on the gbxml output of revit.
>>
>> DesignBuilder is the tool that I use most now in both SBEM (UK regulations
>> format) and EnergyPlus for dynamic modelling. It takes a lot of the best
>> features of both IES and TAS and then adds some other nice touches in terms
>> of data application to speed up the process of setting up your models. The
>> only sticking point with it is that EnergyPlus is painfully slow. The main
>> thing I’d like is for that to be changed and improved. Carrying out
>> simulations with all the lighting controls and calculated natural
>> ventilation turned on for buildings with over 100 zones is nigh on
>> impossible as I don’t fancy leaving it running for a week or two. I have to
>> carry out major sub-division of models or calculate individual zones then
>> schedule up the vent based on those results or just go with scheduled vent.
>> Thankfully the reporting methodology from DesignBuilder is pretty good,
>> though I have to admit I quite like some of the report wizard output by
>> equest.
>>
>> The main advantage of the commercial tools as opposed to the free tools
>> such as DOE and equest, is that they use an interactive 3d model to input
>> the building and that you can interrogate much more easily for
>> post-processing. This means you gain an understanding of the building form
>> much more easily and many link with other tools for further analysis. I like
>> some of what equest has to offer, but I much prefer the interactive model
>> building tools that IES, TAS and DeisgnBuilder offer. They just make
>> it...easier...and generally quicker and more efficient when you consider the
>> other studies that you can do (e.g daylighting, CFD, etc).
>>
>> In terms of asking for changes – having worked for IES (and with many
>> other developers), the stock answer even to their own team was...yes it’s on
>> the list. My guess is that will still be the same.
>>
>> Regards
>>
>> Paul
>>
>>
>>
>> Dr Paul Carey
>>
>> Director
>>
>> Low Carbon Energy Assessor
>>
>>
>>
>> Zero Energy Design Ltd
>>
>> 10A Portland Place
>>
>> 2-22 Mottram Road
>>
>> Stalybridge
>>
>> SK15 3AD
>>
>> T: 0161 3386200
>>
>> F: 0161 3031281
>>
>> M: 0789 4098012
>>
>>
>>
>> E: paul at zed-uk.com
>>
>> W: www.zed-uk.com
>>
>>
>>
>>
>>
>> Certificate No: GB16647
>>
>>
>>
>> Certificate No: GB16646
>>
>>
>>
>> Please carefully consider the environment before you print this email.
>>
>> Company Registered in England & Wales. Registration No. 5815068
>>
>> Registered Address: 10A Portland Place, 2-22 Mottram Road, Stalybridge,
>> SK15 3AD, UK.
>>
>> _Privilege and Confidentiality Notice:___
>>
>> This email and any attachments to it are intended only for the party to
>> whom they are addressed. They may contain privileged and/or confidential
>> information. If you have received this transmission in error, please notify
>> the sender immediately and delete any digital copies and destroy any paper
>> copies. Thank you.
>>
>> *From:* bldg-sim-bounces at lists.onebuilding.org [mailto:
>> bldg-sim-bounces at lists.onebuilding.org] *On Behalf Of *Karen Walkerman
>> *Sent:* 25 February 2009 23:06
>> *To:* Varkie C Thomas
>> *Cc:* Varkie Thomas; bldg-sim at lists.onebuilding.org
>> *Subject:* Re: [Bldg-sim] IES-VE Energy
>>
>> Varkie,
>>
>> I disagree with your statement that eQuest is not appropriate for large
>> buildings because you can't change space names to match architectural names
>> in wizard mode, and the inputs created from the wizard aren't appropriate
>> for all spaces. The wizards are called "Schematic Design Wizard" and "Design
>> Development Wizard" for a reason. They aren't desinged for detail, they're
>> designed to help you make big design decisions quickly. If you want the
>> building to be modeled as closely as possible to the final design, this
>> takes some extra work. Yeah, re-naming spaces is a pain, but at 5 seconds
>> per space, re-naming 1,000 spaces takes about 1.5 hours, well worth the
>> effort. If you re-name zones too, maybe it's 3 hours total.
>>
>> Yeah, some things about eQuest are clumsy, like why does it create one
>> underground wall (and floor) consturction for each surface, when only 4-5
>> are needed for the whole model? Why does it re-create occupancy, lighting
>> and micellaneous equipment schedules for each shell, even if the use is the
>> same? And why does it create tons of duplicate infiltration schedules?
>> BUT... this takes an hour or two to clean up, and then you have a decently
>> flexible model that gives you reasonable results in a matter of minutes.
>> Versus a program that takes 1-2 hours to run. I've done a few LEED projects
>> in Trace700 and it's painful modeling a design case and four (rotated) base
>> cases at 1-2 hours each, especially if you then find you've left anything
>> out.
>>
>> I definitely agree that there are some major things missing in all
>> modeling programs, which is why I'm putting together a "Master Wish List" of
>> modeler's desires. If you have things that you would like to be able to
>> model, things you'd like to be able to model more easily, or things that you
>> can do that you feel are very important, please send me your list. I
>> currently have contact info for about 10 people representing various
>> simulation programs who want to know what we want! Now's our chance to have
>> some input!
>>
>> --
>> Karen
>>
>>
>> On Wed, Feb 25, 2009 at 2:15 PM, Varkie C Thomas <thomasv at iit.edu<mailto:
>> thomasv at iit.edu>> wrote:
>>
>> Graham,
>>
>> The comment below stands out which might also be the reason for not using
>> EnergyPlus on large projects.
>>
>> - DOE-2.2 runs much quicker. For comparable 30,000 m2 buildings I would
>> say DOE-2 runs in 1 minute and IES VE with an APhvac network probably 1-2
>> hours. If you through in Macroflo it probably adds another hour of
>> simulation time. As a result *iterative trial and error debugging* has to be
>> done on a 1-2 week period.
>>
>> Large building projects (1 to 10 million sqft) with up to 1,000 zones and
>> 70 systems ranging in size from 10,000 to 200,000 cfm (pardon the English
>> units - the USA & the Bahamas are not going to switch to metric) require
>> several iterative runs to get the input errors fixed. Breaking up the
>> project into small pieces is not a solution since it affects demand costs,
>> central plants and other components. I have worked on such projects using
>> DOE2.1E and TRACE600/700.
>>
>> eQUEST is not suitable for such projects either. One of its limitations is
>> that you cannot enter the space names shown on architectural drawings.
>> Others include assuming all the input data and making all the decisions for
>> you when you enter the type of building. 1000 zones means 1000 infiltration
>> schedules and multiples of other building components. It is unrealistic to
>> check all the input created by eQUEST for errors. Fixing everything to match
>> the exact project data has to be done in detailed edit. Detailed edit means
>> you lose access to the graphical method of creating the building model from
>> AutoCAD drawings which is the main benefit of this program.
>>
>> Varkie
>>
>> ------------------------------------------------------------------------
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send a blank message to
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>> ------------------------------------------------------------------------
>>
>>
>> No virus found in this incoming message.
>> Checked by AVG - www.avg.com Version: 8.0.237 / Virus Database:
>> 270.11.3/1971 - Release Date: 02/25/09 06:40:00
>>
>>
>>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090226/61b3584c/attachment-0001.htm>
More information about the Bldg-sim
mailing list