[Bldg-sim] CFD Analysis
Shishir Gupta
shishir at mechartes.com
Fri Feb 27 23:52:26 PST 2009
Carney,
I'm also among the group of people who are not too comfortable with CFD
results from tools like IES-VE and Designbuilder. These are primarily energy
modeling tools with built in CFD applications. However they provide a
seamless environment (for Energy modeling and CFD) and have easy to
understand user interface but I feel the main problem is with 'automatic
meshing' that these software offer. Meshing is a critical component of the
CFD process and it would be hard to automatically generate right kind of
mesh for infinite variations of geometry and operating conditions.
To obtain correct CFD results we must check mesh convergence, may be these
tools have algorithm which create very fine mesh to start with and hence
they take a long time to produce results. Improving hardware capacity like
JRR and Zhoulum suggested is essential but its also critical to create right
kind of mesh to get quick results. This is especially critical for building
application since the volume of analysis zone is usually huge, if we mesh it
improperly then we can end up waiting for an year even on 32 machine cluster
or a powerful Xeon server.
In my opinion also stand alone CFD tools like Fluent, Phoenics, CFX, StarCD
etc. are much better CFD tools than IES-VE. Even if you would like to
use IES-VE it would be prudent to test a few cases of your analysis and
compare results with established stand alone CFD tools.
There are also CFD tools specific for building applications like
Fluent-Airpak and Flovent which are customized for building applications.
These tools are easy to understand for building engineers and produce good
results. Another good option can be OpenSource CFD libraries like OpenFoam,
FDS etc. However the problem there is that learning curve with OpenSource
platforms is rather slow.
Regards
Shishir
------------
www.mechartes.com
2009/2/27 CARNEY Ronan <Ronan.CARNEY at projectservices.qld.gov.au>
>
> Dear all,
>
> I am writing to you to ask for your personal preference on which CFD
> software package I should use for all the following (as one) and your reason
> why;
>
> A) Large Scale City Analysis of wind turbulence and velocity
> B) Internal and external analysis (combined)
> C) CFD for Urban Design.
>
> Currently we use IES-VE for CFD analysis but from what I've heard, the
> general consensus is that, it may not be near accurate enough. In addition,
> the computational time is far too long.
>
> *Regards,***
> *****Ronan Carney***
> Electrical Engineer
> ***Project Services*
> * Level 5B 80 George St Brisbane
> ( Ph: (07) 3224 5983
> 2 Fax: (07) 3224 6151
> ,Email:*** **Ronan.Carney at projectservices.qld.gov.au***<Ronan.Carney at projectservices.qld.gov.au>
> **
> [image: Picture (Metafile)]****
> “*Queensland celebrates its 150th birthday throughout 2009.*
> *Check out what's on today at **www.q150.qld.gov.au*<http://www.q150.qld.gov.au/>
> *.”*
>
> ***************************** Disclaimer *****************************
>
> The contents of this electronic message and any attachments are intended
> only for the addressee and may contain privileged or confidential
> information. They may only be used for the purposes for which they were
> supplied. If you are not the addressee, you are notified that any
> transmission, distribution, downloading, printing or photocopying of the
> contents of this message or attachments is strictly prohibited. The
> privilege of confidentiality attached to this message and attachments is not
> waived, lost or destroyed by reason of mistaken delivery to you. If you
> receive this message in error please notify the sender by return e-mail or
> telephone.
>
> Please note: the Department of Public Works carries out automatic software
> scanning, filtering and blocking of E-mails and attachments (including
> emails of a personal nature) for detection of viruses, malicious code, SPAM,
> executable programs or content it deems unacceptable. All reasonable
> precautions will be taken to respect the privacy of individuals as outlined
> in the DPW Privacy Plan. Personal information will only be used for official
> purposes, e.g. monitoring Departmental Personnel's compliance with
> Departmental Policies. Personal information will not be divulged or
> disclosed to others, unless as required by Departmental Policy and/or State
> or Commonwealth Law.
>
> Thank you.
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090228/d3e0b542/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/bmp
Size: 24330 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090228/d3e0b542/attachment-0002.bin>
More information about the Bldg-sim
mailing list