[Bldg-sim] System Fan Power in Appendix G
Sam Mason
sam.mason at atelierten.com
Tue Jan 27 13:58:56 PST 2009
Molly,
Thanks for your input. I agree with your interpretation of the code.
Supply fan CFM should be used, with applicable pressure credits, to
determine the entire baseline HVAC system fan brake HP, which is then
split amongst the supply/return/exhaust fans. My interpretation was
trying to get at lab building modeling which in some cases have separate
AHUs for return systems.
Another question to everyone then: How do you deal with labs which have
extremely high fan HP to overcome the large static pressure typical of
this building type? This has been a topic of conversation before but
would like to know from experience what the calculations have shown.
My example: a current lab building has several large AHU providing
80,000 CFM each with 200 HP fan motors. The return systems are the same
size, so each AHU has a total of 400 HP of fan power. Following
90.1-2007 and using total static pressure credits of 9.5 in. wc, the
baseline system fan power is only 288 HP. There is no way to meet code
and overall the proposed building is barely saving any energy over the
baseline building.
Sam
--
Sam Mason
Atelier Ten
sam.mason at atelierten.com
-----Original Message-----
From: Molly Curtz [mailto:molly.curtz at arup.com]
Sent: Tuesday, January 27, 2009 2:03 PM
To: George Hu; Sam Mason; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] System Fan Power in Appendix G
George and Sam,
I may just misunderstand what you are saying, but I suspect you may not
be reaching a correct conclusion. Whether the fans are modeled
separately or together, the baseline fan power allowance covers all the
fans in the system (I divide this among the various fans based on the
proposed system fan power ratios of supply to return, etc).
As Bill Talbert mentioned earlier in this thread, look at Addendum ac to
90.1-2004. Specifically read through the definitions of "fan system bhp"
or "fan system motor nameplate hp" therein which should clarify that the
hp allowance values are for "all fans that are required to operate at
design conditions to supply air from the heating or cooling source to
the conditioned spaces and return it to the source or exhaust it to the
outdoors".
I hope this helps to clarify things.
Kind Regards,
Molly Curtz, P.E.
Mechanical Engineer
Arup
403 Columbia St., Suite 220
Seattle, WA 98104
direct: 206 493 2234
tel: 206 749 9674 ext. 25534
fax: 206 749 0665
molly.curtz at arup.com
www.arup.com
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of George Hu
Sent: Tuesday, January 27, 2009 6:27 AM
To: 'Sam Mason'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] System Fan Power in Appendix G
I agree with you, Sam. The supply, return and relief fans need to be
modeled separately, which I believe fits the intent of comparing the
efficiencies of the fans between "Proposed"
and "Baseline" and also
informs you where to improve for your "Proposed" design in terms of fan
power consumption.
George Hu, PE, LEED AP
President
AWE | Air Water Energy Engineers, Inc.
781.652.8688
www.awe-e.com
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Sam Mason
Sent: Thursday, January 22, 2009 11:31 AM
To: Bill Talbert; bldg-sim at lists.onebuilding.org; Kendra Tupper; Mike
Kaufman; Ming Zeng
Subject: Re: [Bldg-sim] System Fan Power in Appendix G
Section G3.1.2.8 says "if return or relief fans are specified in the
proposed design, the baseline design shall also be modeled with fans
serving the same function and sized for the baseline system supply fan
air quantity less then minimum outdoor air, or 90% of the supply fan air
quantity, whichever is larger."
This would lead me to believe that you need to specifically model
return/exhaust/relief fans the same as supply fans and not group
everything together. Section G3.1.2.9 is written poorly because it
calls out "supply CFM," but should be applicable to all types of fans.
Comments?
Sam
--
Sam Mason
Atelier Ten
sam.mason at atelierten.com
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Bill
Talbert
Sent: Tuesday, January 20, 2009 1:54 PM
To: bldg-sim at lists.onebuilding.org; Kendra Tupper; Mike Kaufman; Ming
Zeng
Subject: Re: [Bldg-sim] System Fan Power in Appendix G
Make sure you look at Addendum AC if you are using A90.1-2004. The
calculation and pressure credits have changed, but it is still
consistent with your Option 1 description.
Bill Talbert, PE, LEED(r) AP
Mechanical Systems
Phone: (608) 441-6677
E-mail: btalbert at aeieng.com
Affiliated Engineers Inc.
5802 Research Park Blvd.
Madison, WI. 53719
Tel. (608) 238-2616
Fax. (608) 238-2614
>>> Kendra Tupper <ktupper at rmi.org> 1/20/2009 12:42 PM >>>
Option 1 - the user's manuals are a bit more clear, and specify that the
its is the supply cfm that should be used to calculate the fan power.
This fan power includes supply, return and exhaust.
On 1/20/09 11:29 AM, "Zeng, Ming" <mzeng at leoadaly.com> wrote:
My understanding is option 1. The fan energy in that formula is the sum
of all the fan horse power. Search the board, I think there is a
previous email from Michael Rosenberg talking about the fan energy. Hope
this helps.
Ming Zeng, PE, LEED(r) Accredited Professional
Mechanical Engineer
730 Second Avenue South, Suite 1100, Minneapolis, MN 55402-2455
T 612.338.8741 F 612.338.4840 D 612.341.9539
www.leoadaly.com <http://www.leoadaly.com> MZeng at leoadaly.com
Please consider the environment before printing.
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Mike
Kaufman
Sent: Tuesday, January 20, 2009 12:16 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] System Fan Power in Appendix G
Hi All,
I have a specific question about using Appendix G3.1.2.9 to calculate
baseline system fan power (I have already searched previous posts and
could not find the answer I'm looking for). So, the Appendix G section
reads as
follows: System fan electrical power for supply, return, exhaust, and
relief (excluding power to fan powered VAV boxes) shall be calculated
using the following formulas. I understand the formulas, which
essentially use a fan CFM to determine a brake horsepower BHP, which is
then used to calculate the fan power (Watts), but my question is this:
Supposing you have an HVAC system with supply, return, and small exhaust
fans (in restrooms, for
example) - how do you calculate the power to each fan?
Option 1: Use your supply fan cfm to calculate a power, say it comes to
10 kW, and use this as your total "system" fan power. This 10 kW, being
your whole system power, is then distributed among all of your system
fans however you desire (For example, supply fan power = 5 kW, return
fan power =
4 kW, exhaust fan power = 1 kW, for a total of 10 kW for the fan system)
OR
Option 2: Use each supply, return, and exhaust fan cfm to separately
calculate an individual kW for each fan (For example, supply fan power =
10 kW using the supply cfm, return fan power = 9 kW using the return
cfm, exhaust fan power = 1 kW using the exhaust cfm, for a total of 20
kW for the whole fan system)
Obviously, you will have much more fan energy in a baseline system
calculating fan power with Option 2. Does anyone have a specific
example they can share of a fan system calculation that was accepted by
USGBC for an
EAc1 energy model?
Thanks for your help!
Mike
Mike Kaufman, Building Performance Engineer 130 W. 5th Avenue,
Denver, CO 80204 (NOTE NEW ADDRESS) t 303.278.1532x206 | f 303.278.8533
| ambient-e.com <http://www.ambient-e.com/>
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
________________________________________________________________________
This e-mail has been scanned for all viruses by Star. The
service is powered by MessageLabs. For more information on a proactive
anti-virus service working around the clock, around the globe, visit:
http://www.star.net.uk
________________________________________________________________________
______________________________________________________________________
This email has been scanned by the MessageLabs Email Security System.
For more information please visit http://www.messagelabs.com/email
______________________________________________________________________
More information about the Bldg-sim
mailing list