[Bldg-sim] Modeling Baseline Exterior wall for Renovation
Gregg Liddick
gliddick at theepstengroup.com
Mon Jan 12 14:01:01 PST 2009
It seems like you're thinking of what needs to be done for district energy.
According to ASHRAE 90.1-2004 Appendix G, "For existing building envelopes, the baseline building design shall reflect existing conditions prior to any revisions that are part of the scope of work being evaluated".
You may be right in that it's been changed in a CIR, although they tend to make things easier for the project team most of the time.
Gregg Liddick
________________________________
From: bldg-sim-bounces at lists.onebuilding.org [bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Alex Chapin [alexc at 2rw.com]
Sent: Monday, January 12, 2009 3:32 PM
To: bldg-sim at lists.onebuilding.org
Cc: Allison_Gaiko at aha-engineers.com
Subject: [Bldg-sim] Modeling Baseline Exterior wall for Renovation
The way it works is as follows:
-Step 1, Compare proposed model to baseline model with existing wall and use this to achieve points
(p. 181 of LEED NC 2.2 EA Credit 1 Calculations Section)
-Step 2, Compare proposed model to baseline model with ASHRAE 90.1 walls as a check to make sure proposed is at least this efficient
(At the moment I can’t remember where I read this, maybe a CIR? Can anyone confirm this?)
Alex Chapin, E.I.T., LEED AP
Energy Engineer
2rw Consultants
T: 434-296-2116 ext. 101
F: 434-977-1862
Date: Mon, 12 Jan 2009 10:49:36 -0500
From: "Gaiko Allison" <Allison_Gaiko at aha-engineers.com>
Subject: [Bldg-sim] Modeling Baseline Exterior wall for Renovation
To: <bldg-sim at lists.onebuilding.org>
Message-ID:
<3C61A3A4F1F6F045858CAB5C84CDDCF7040B8FDE at fs7.aha-engineers.com>
Content-Type: text/plain; charset="us-ascii"
I am working on a renovated building and am wondering whether the
baseline exterior wall should be the current existing wall or the
baseline wall system as described by ASHRAE 90.1. If it matters, we are
going for LEED NC points because of the extent of the renovation, not
LEED EB.
Does anyone have any experience with this?
Allison Gaiko, PE, LEED AP
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090112/0941f4f2/attachment-0002.htm>
More information about the Bldg-sim
mailing list