[Bldg-sim] Modeling a natatorium using Appendix G and eQUEST
    Bishop, Bill 
    bbishop at PathfinderEngineers.com
       
    Fri Mar 20 05:47:19 PDT 2009
    
    
  
  
Greg,
 
I think you need to add DX cooling to your proposed design, and energy
recovery to your baseline. Table G3.1 10.(d) states that, "where no
cooling system exists or no cooling system has been specified, the
[proposed] cooling system shall be identical to the system modeled in
the baseline building design." See G3.1.2.10 Exhaust Air Energy Recovery
to determine if it is required or not. I believe you meet the 5000 cfm
supply air and 70% OA criteria. Make sure none of the exceptions apply.
 
Regards,
Bill
 
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
bbishop at pathfinderengineers.com
 
www.pathfinderengineers.com
P Please strive to live sustainably.
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Greg
Schlegel
Sent: Thursday, March 19, 2009 7:39 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Modeling a natatorium using Appendix G and eQUEST
 
We're working on a building that has a large natatorium.
The project is located in Utah so we can use outside air for
dehumidification.  There is no mechanical cooling in the as-designed
system.
 
Per Appendix G, it appears that the baseline system should be a packaged
single zone unit with a fossil fuel furnace for heating, an air side
economizer (dry bulb high limit of 75 F), and DX cooling.  We're
controlling the space temp at 88 F and the relative humidity between
40-60%.  The baseline system would run as a constant volume unit with a
minimum ventilation air requirement of 0.5 cfm/sf (~15,000 cfm).   
The Appendix G baseline system has a considerable dehumidification load
- which shows up as a cooling energy.
 
The as designed system is a heating only unit with an air side
economizer and heat recovery.  The system uses outside air to dehumidify
instead of a DX coil (Utah has a very dry climate).  Space conditions
remain the same.  We've modeled this system by increasing the amount of
ventilation air delivered to the space until the relative humidity in
the space is between roughly 40 and 60%. 
 
The results show a large electric fan penalty (due to the pressure drop
across the heat recovery), a large amount of heating savings (from the
heat recovery), and a large amount of cooling savings, since we're now
using OA, heat recovery and natural gas to dehumidify the space instead
of electricity.
 
Is this a reasonable approach per the Appendix G modeling methodology?
It seems unreasonable to us that we should be able to claim the
cooling/dehumidification savings, but per Appendix G this seems to be
the case.  I would welcome any and all thoughts and feedback.
 
Thanks.
 
Greg Schlegel
Energy Analyst, PE, LEED-AP 
 
 
------------------------------------------------------------------------
----------------
CONFIDENTIALITY NOTICE This e-mail transmission, and any documents,
files or previous e-mail messages attached to it may contain
confidential information that is legally privileged. If you are not the
intended recipient or the person responsible for delivering it to the
intended recipient, you are hereby notified that any disclosure,
copying, distribution or use of any of the information contained in or
attached to this transmission is strictly prohibited. If you have
received this transmission in error, please immediately notify us by
telephone at (801) 278-1927 and destroy the original transmission and
its attachments without reading them. Thank you. 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090320/5cf03eb9/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3728 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090320/5cf03eb9/attachment-0002.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 92 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090320/5cf03eb9/attachment-0002.gif>
    
    
More information about the Bldg-sim
mailing list