[Bldg-sim] Therapy Pool Simulation
Bishop, Bill
wbishop at pathfinder-ea.com
Tue Nov 3 05:00:38 PST 2009
Larry,
I've modeled a natatorium in TRACE but it shouldn't be a problem in
eQUEST. The pool is a latent load on the space and also a water heating
load. You will need to know/select the water temperature, space
temperature, space humidity and ventilation rate. I suggest using the
ASHRAE Handbook - Applications p4.6 for guidance, as well as product
literature for natatorium air handling systems. For water heating, you
will have to make up the latent load as well as account for
emptying/refilling the pool for regular cleaning.
Regards,
Bill
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jeff Haberl
Sent: Monday, November 02, 2009 9:29 PM
To: 'lasmith_architect.leed at yahoo.com'; 'bldg-sim at lists.onebuilding.org'
Subject: Re: [Bldg-sim] Therapy Pool Simulation
FYI.
We tried to simulate this back in 1985 with DOE-2 by forcing the loads
to equal measured amounts and got somewhat close. Measured data included
the pool evaporation rate and ice rink refrigeration load. This was
published in an ASHRAE Transactions paper.
Also, there are some papers published on predicted evaporation rates
from exposed pools. Several are listed in the apx to the FCHART manual.
Otherwise, you can guess.
Jeff
BB 8=! 8=) :=) 8=) ;=) 8=) 8=( 8=) :=') 8=) 8=) 8=? BB
Jeff S. Haberl, Ph.D., P.E.,
FASHRAE...................jhaberl at esl.tamu.edu
Professor......................................................Office
Ph: 979-845-6507
Department of Architecture.......................Lab Ph: 979-845-6065
Energy Systems Laboratory.......................FAX: 979-862-2457
Texas A&M University..............................77843-3581
College Station, Texas, USA.......................URL: www-esl.tamu.edu
BB 8=/ 8=) :=) 8=) ;=) 8=) 8=() 8=) 8=? 8=) 8=) 8= BB
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
<bldg-sim-bounces at lists.onebuilding.org>
To: bldg-sim at lists.onebuilding.org <bldg-sim at lists.onebuilding.org>
Sent: Mon Nov 02 18:17:15 2009
Subject: [Bldg-sim] Therapy Pool Simulation
Has anyone used EQUEST to simulate an indoor pool or therapy pool
performance? If so please provide some pointers. If not what program
would you suggest using?
Larry Smith
Architect Energy Consultant
lasmith_architect.leed at yahoo.com
<mailto:lasmith_architect.leed at yahoo.com>
phone 206-218-2572
fax 206-905-0812
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091103/d42d1bde/attachment-0001.htm>
More information about the Bldg-sim
mailing list