[Bldg-sim] Ground Source Water-to-Water HP in eQuest
Anthony Hardman
Anthony at geoenergyservices.com
Tue Nov 3 09:03:55 PST 2009
If you don't want to use outside programs to estimate the ground heat
exchanger response, you can input the condenser loads directly into the
ground heat exchanger water loop as a process load.
For GSHP's, just make sure you're using heat of extraction spec data for
your condenser loads, not total heating capacity.
Integrating the loads from multiple systems (DHW, Bldg, et. al.) into a
single GHX also yields a more cost effective (fewer bores) GHX from an
installation perspective.
Anthony Hardman
Mechanical Engineer
Geo-Energy Services
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Tuesday, November 03, 2009 8:37 AM
To: Jackson, Alan
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Ground Source Water-to-Water HP in eQuest
That's pretty much what I've done for a few projects.
1. Calc your loads incident on the loop, either using eQuest or
another program
2. Use those loads to determine the annual thermal behavior of the
ground loop using a program like the free GS2000 or a similar ground-loop
design tool.
3. Use the thermal behavior output of your ground-loop software of
choice to create a custom temperature schedule. If you want a more detailed
explanation of the step-by-step process within eQuest, search for my name in
the eQuest/Bldgsim archives.
~Nick
cid:489575314 at 22072009-0ABB
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Jackson, Alan
Sent: Tuesday, November 03, 2009 9:20 AM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Ground Source Water-to-Water HP in eQuest
I believe the methodology that has been implemented with success is to use
the WTW HPs with the lake well, but to use a schedule for well water
temperatures either taken from a separate run with WTA and closed loop, or
to take the temperatures from another yearly sim in either GLHE-PRO or
GS2000.
Alan Jackson, LEED AP
KlingStubbins
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Garcia, Robert
Sent: Tuesday, November 03, 2009 10:04 AM
To: 'bldg-sim at lists.onebuilding.org'
Subject: [Bldg-sim] Ground Source Water-to-Water HP in eQuest
This topic appears to be a gray area within eQUEST. Has anyone been able to
successfully model a Ground Source Water-to-Water HP connected to a closed
loop Geothermal Well Field?
The WWHP is to serve a radiant floor. In addition to the WWHP, the design
also has multiple Water-to-Air Heat Pumps connected to the same well field.
Issues rise when trying to figure out how to model the effect of the WWHP on
the Well Loop.
In the past I have used the Loop-to-Loop Chiller to model a WWHP, but the
chiller requires a connection to a Lake-Well type loop.
Thanks in advance.
Robert Garcia |AKF|
This e-mail may contain information that is confidential, privileged or
otherwise protected from disclosure. If you are not an intended recipient of
this e-mail, do not duplicate or redistribute it by any means. Please delete
it and any attachments and notify the sender that you have received it in
error. Unintended recipients are prohibited from taking action on the basis
of information in this e-mail. E-mail messages may contain computer viruses
or other defects, may not be accurately replicated on other systems, or may
be intercepted, deleted or interfered without the knowledge of the sender or
the intended recipient. If you are not comfortable with the risks associated
with e-mail messages, you may decide not to use e-mail to communicate with
AKF.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091103/bbfaebdf/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091103/bbfaebdf/attachment-0002.jpeg>
More information about the Bldg-sim
mailing list