[Bldg-sim] Ashrae 90.1 - Unmet hours
    Seth P. Spangler 
    sspangle at rmf.com
       
    Tue Oct 27 04:34:23 PDT 2009
    
    
  
Am I missing something or does this table and the corresponding answer
(7 unmet hours) not make sense.
 
Zone 1 unmet during:                        6          8          14
16
Zone 2 unmet during:                        6          8          12
16
Zone 3 unmet during:                        7          8          12
13
 
If the columns (hours outside of throttling range) all represent
simultaneous hours in the model then wouldn't the total number of hours
be the sum of the maximum number of hours for each time period?
(7+8+14+16=45 hours outside of range) I have looked at the chart
multiple ways and do not see how seven (7) could ever be the correct
value.
 
Yes, projects with hundreds of zones may be penalized however ASHRAE
allows similar spaces(orientation, load , HVAC system) to be combined
into a single zone which can reduce the impact of this issue.
 
I personally sum all of the hours ANY zone is outside of range without
regard to when the time period is. I feel that this is the most accurate
method of correctly sizing the HVAC systems.
 
Seth Spangler, LEED(r) AP 
Project Engineer
 
RMF Engineering, Inc 
Ph: (843) 971-9639 ext:1497
Fax: (843) 971-9641 
sspangle at rmf.com
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of ashu gupta
Sent: Tuesday, October 27, 2009 1:17 AM
To: 'Rosenberg, Michael I'; 'Nick Caton'; 'Crockett, Jim'; 'Kendra
Tupper'
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Ashrae 90.1 - Unmet hours
 
Dear All,
 
Explanation of Unmet Hours is as follows:
 
Unmet Hours:
Unmet hours of a building are the summation of the number of hours when
the heating or the cooling set point temperature of a zone is not met
either by the HVAC system or by the plant.
Understanding/Interpreting/Calculating the number of unmet hours:
*	Unmet hour is for a particular zone when the zone indoor
temperature is higher than the heating or cooling set point specified in
that hour.
*	The number or the percentage of unmet hours in a building is
usually given as one of the outputs of the simulation.
*	Zone wise unmet can also be read from the various output files
provided by the software used for simulation.
(Example:  
Visual DOE: "SS-J System Peak Heating and Cooling Days" report &
Energy Plus: Output Variable, "Time Cooling Set point Not met")
*	When two zones are unmet at the same hour, this will count to
one unmet hour for the building.
*	When two zones have unmet hours during different non overlapping
times of a day, the total number of unmet hours in that day is the
summation of these unmet hours of each zone. This total for the year
should be considered as the total unmet hours of the building.
Example: 
When each zone is unmet in the specified hours as beside,
 
Zone 1 unmet during:                        6          8          14
16
Zone 2 unmet during:                        6          8          12
16
Zone 3 unmet during:                        7          8          12
13
            
Total number of unmet hours of the building: 7 hrs and not 12hrs.
6          7          8          12        13        14        16
 
*	When percentage of unmet is specified, than this is the
percentage of total number of hours (1 year- 8760 hours) for which the
simulation is performed (not just the occupied hours)
*	As per ASHRAE 90.1-2004, the unmet hours of the total building
should be less than or equal to 300 hours and the difference in the base
case and proposed case should be less than or equal to 50 hours.
*	If unmet load hours in the proposed building exceed the unmet
load hours in the baseline building by more than 50, then the size of
equipment in the baseline building shall be reduced incrementally, until
the condition is satisfied.
 
 
Thanks
Ashu Gupta,
Project Engineer,
Kamal Cogent Energy,
Kamal Ratan Chanbers 1st Floor,
Opp. GPO, M.I. Road,
Jaipur 302001
Ph 141 2373185(W)
Ph 9251665008(M)
kce2 at kamalcogentenergy.com <mailto:kce2 at kamalcogentenergy.com> 
www.kamalcogentenergy.com <http://www.kamalcogentenergy.com> 
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rosenberg,
Michael I
Sent: Tuesday, October 27, 2009 9:07 AM
To: Nick Caton; Crockett, Jim; Kendra Tupper
Cc: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Ashrae 90.1 - Unmet hours
 
I think eQuest and any DOE2 based software does report the hours of
loads not being met as required by Appendix G. In the BEPS report it
gives "PERCENT OF HOURS ANY SYSTEM ZONE OUTSIDE OF THROTTLING RANGE". My
understanding of this number is that it is a percentage of scheduled fan
run-time hours, so some calculation may be necessary.
 
__________________________ 
Michael Rosenberg 
Senior Commercial Buildings Energy Analyst 
ENERGY & ENVIRONMENT DIRECTORATE 
Pacific Northwest National Laboratory 
2032 Todd Street 
Eugene, OR 97405 
(541) 844-1960 
michael.rosenberg at pnl.gov 
www.pnl.gov 
From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: Monday, October 26, 2009 8:20 PM
To: Rosenberg, Michael I; Crockett, Jim; Kendra Tupper
Cc: bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Ashrae 90.1 - Unmet hours
 
Mike,
 
I appreciate you bringing this up.  This definition drives straight to
the heart of defining the issue-at-hand...  Since I kinda presented both
sides of the issue at once - I'd like to clarify where I stand regarding
what the correct interpretation should be.  
 
The logic is as follows:  If a modeled year has 8,760 hours, can there
be 10,000 unmet load hours?  By strict reading of the standard's
definition below, I would put my foot down stating there can only be
8,760, at most.  
 
By common practice however, it appears a majority (myself included) sum
unmet cooling/heating hours between the zones, even if they should fall
on the same modeled hour, against the intent of the standard.  
 
My pure speculation (for what it's worth, as a young EIT) is this
practice developed because eQuest BDL reports don't present the crunched
numbers in a way that makes the sum of unmet load hours, as intended by
90.1, easy to determine.  I wouldn't be shocked to learn other energy
modeling software packages generate LEED compliance summaries featuring
unmet load hour totals in sync with the real intent of ASHRAE 90.1.
 
If there's anything I've learned from going out on a limb, it's that I'm
sure to learn something whether I fall or not!
 
~Nick
 
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
 
From: Rosenberg, Michael I [mailto:michael.rosenberg at pnl.gov] 
Sent: Monday, October 26, 2009 7:39 PM
To: Nick Caton; Crockett, Jim; bldg-sim at lists.onebuilding.org
Subject: RE: [Bldg-sim] Ashrae 90.1 - Unmet hours
 
Nick,
 
Your interpretation is the correct one. According to the definitions in
Standard 90.1.
unmet load hour: an hour in which one or more zones is outside of the
thermostat setpoint range.
 
 
Mike
__________________________ 
Michael Rosenberg 
Senior Commercial Buildings Energy Analyst 
ENERGY & ENVIRONMENT DIRECTORATE 
Pacific Northwest National Laboratory 
2032 Todd Street 
Eugene, OR 97405 
(541) 844-1960 
michael.rosenberg at pnl.gov 
www.pnl.gov 
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Nick Caton
Sent: Monday, October 26, 2009 5:33 PM
To: Crockett, Jim; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Ashrae 90.1 - Unmet hours
 
Jim,
 
That's actually a really good question that I was afraid to ask when I
first encountered it - kudos to you!  I've currently resolved to follow
what others seemed to be doing within and outside of my office:  Sum up
all unmet hours for cooling and heating between the zones just as you
describe.   In your example, I'd agree that the unmet hours of your 301
zone building total 301.
 
I do agree that this doesn't seem intuitively to be the intent of the
standard, however between what is suggested within 90.1, the LEED
handbook, and the LEED credit templates - I honestly can't see any clear
indication either way on which is the appropriate interpretation.  
 
I think the appropriate metric for ensuring appropriately sized systems
should be something like: "hours of the modeled year in which at least
one zone has an unmet cooling/heating load,"  but I think that was
avoided by all concerned parties because it's too wordy!
 
My acting interpretation, again referencing your example, is that all
systems of your 301 zone example affecting the zones with unmet
cooling/heating hours should have their heating/cooling/overall sizing
capacity ratios increased incrementally until the design hours fall
below 300 (and/or within 50 of the sum from the other model, depending
on your situation).
 
Afraid I'm only really adding to the discussion here without providing a
solid answer.  Would like to echo the desire to see anyone's experiences
that would help us know the "right" way to interpret this (in my case,
specifically in the context of a LEED submittal).
 
 
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
 
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Crockett,
Jim
Sent: Monday, October 26, 2009 4:27 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Ashrae 90.1 - Unmet hours
 
Ashrae 90.1 (2004) Appendix G3.1.2.2 requires a baseline building to
have less than 300 unmet hours.  What exactly does this mean?
 
To illustrate my question:  assume you have a building with 301 zones,
and each zone has 1 unmet hour per year.  This gives you a total of 301
unmet hours, and requires you to increase your baseline equipment
capacity.  But you could argue that, on average, the building has only 1
unmet hour per year.
 
Have any of you run into this?  Is it addressed in an addendum
somewhere, etc?
 
Any help is appreciated.  Thanks,
 
 
 
Jim Crockett, P.E.
 
Senior Project Engineer
Energy & Carbon Management
Nexant, Inc.
4021 S. 700 E., Suite 250
Salt Lake City, Utah 84107
 
(801) 639-5603 - phone
(801) 266-4786 - fax
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091027/c1870525/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20091027/c1870525/attachment-0001.jpeg>
    
    
More information about the Bldg-sim
mailing list