I looked this up just recently...this is what I found from an old post:
Bryce,
The CEC method is required for compliance purposes, but many use simpler
methods such as converting the SEER to EER by using a multiplier (0.85  to
0.95 are often used) and then converting the EER (95/67) to EIR using a
straight unit conversion.  RESNET which is the body that I've worked with on
software verification methods for nationwide HERS ratings for houses uses
the following equation:
Cooling EIR = 0.941 * (1/(SEER/3.413))
This was developed as a simplification to more complex methods and is based
on a regression analysis of numerous systems.  As I'm sure you're aware, the
conversion of SEER to EER is not exact and depends on the means by which the
manufacturer acheived the SEER.
There are then various assumptions about the part load performance of the
units, but that is another topic.
Good luck,
Pat
_______________________
Pat Bailey, P.E.
Principal
GeoPraxis, Inc
205 Keller Street
Petaluma, CA 94952
Andrew Craig, EIT,LEED AP/ Mechanical Designer/ Energy Analyst
INTERFACE ENGINEERING 
direct 503.382.2696
 Please consider the environmental impact before printing this email. 
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Joel Oester
Sent: Friday, September 04, 2009 1:21 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] SEER / EER / EIR Ratings
I am putting together my baseline model for a LEED project and 2004 ASHRAE 90.1 only gives SEER values for units under 65,000 BTU.  In order to model this correctly on eQuest I need both EIR and fan power.  Does anyone know how to get this info from the SEER rating? 
Thanks!
Joel
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
    
    
More information about the Bldg-sim
mailing list