[Bldg-sim] Baseline Efficiencies
    Nikola Kravik 
    nkravik at rumseyengineers.com
       
    Thu Sep 17 16:32:57 PDT 2009
    
    
  
Felipe,
-I think you’re right; Table 6.8.1A shows 9.2 EER which is 2.7 COP on cooling side (sized for electric heat ≥760k).
Nikola
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Thursday, September 17, 2009 3:39 PM
To: bldg-sim at lists.onebuilding.org; Felipe Durán
Subject: Re: [Bldg-sim] Baseline Efficiencies
Felipe:
If I understand you correctly, your Proposed Building has the 500 kW size of heat pump. What goes into the Baseline Case should be the COP based on all of the modeling assumptions from Appendix G and the actual physical configuration of the building, which may or may not be the same size as what is being installed.
Other commenters ??
John Aulbach
Southern California, USA
--- On Thu, 9/17/09, Felipe Durán <felipe at b-green.cl> wrote:
From: Felipe Durán <felipe at b-green.cl>
Subject: [Bldg-sim] Baseline Efficiencies
To: bldg-sim at lists.onebuilding.org
Date: Thursday, September 17, 2009, 12:12 PM
Dear All,
I`m modelling  a 3 floor non-building using the appendix G. According to the size and type of the building,  the baseline HVAC system type would be a "packaged rooftop VAV with reheat" (system 6). The proposed building has a heat pump for heating and cooling of about 500 kW. Does anybody knows about the baseline efficiencies for both cooling and heating? I have checked 90.1 standard and it seems that they would be COP 1 (heating) COP 2.7 (cooling). Am I right?
Thanks,
Felipe Durán Palma
Arquitecto PUC, MPhil. U. Cambridge
Director de Proyectos y Asesorías
[cid:image001.png at 01CA37B4.30F8C090]
Obispo Donoso 5 oficina 62 - Providencia - Santiago
felipe at b-green.cl<http://us.mc528.mail.yahoo.com/mc/compose?to=felipe@b-green.cl> - www.b-green.cl<http://www.b-green.cl/> - 56 (2) 3431868
-----Inline Attachment Follows-----
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG<http://us.mc528.mail.yahoo.com/mc/compose?to=BLDG-SIM-UNSUBSCRIBE@ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090917/395ae2d4/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 9930 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090917/395ae2d4/attachment-0002.png>
    
    
More information about the Bldg-sim
mailing list