[Bldg-sim] Match ventilation rates
B. Fountain
bfountain at greensim.com
Wed Apr 7 12:21:17 PDT 2010
In EE4, the reference and proposed buildings always have the same OA
ventilation rates. By setting the proposed building OA airflow, you are
by definition setting the reference building OA airflow values.
If you require different ventilation rates between proposed and reference
files (e.g. if you have high proposed building airchange rates in excess
of 120% of ASHRAE-62 and need lower values for the reference building per
old CBIP rules), you need to create a separate reference building run with
the different flow rates in the proposed building.
If you are looking at the proposed and reference buildings and are seeing
different OA airflow rate values in the SV-A reports between proposed and
reference then you almost certainly have a zonal type system with heat
recovery, where EE4 is derating the proposed building OA airflows as a
workaround to model the heat recovery.
Feel free to contact to discuss further.
Brian
> Hi all,
>
>
>
> Does anyone know how to change the ventilation rates and/or supply fan
> power
> for the reference building generated automatically by EE4 (DOE based)
> software? I need to change the ventilation rate for my reference building
> to
> match the proposed in order to meet the local code requirements.
>
>
>
> I appreciate any suggestion.
>
>
>
> __________________________________________________________________________
>
> Ahmed Azhari, B.Eng., LEEDR AP
>
> Energy Analyst
>
>
>
> Jain Sustainability Consultants Inc.
>
>
>
> 2260 Argentia Road, 2nd Floor
>
> Mississauga, Ontario L5N 6H7, CANADA
>
> Tel: (905) 542 7211 Ext 234
>
> Fax: (905) 542 7622
>
> Email: <mailto:aazhari at jainconsultants.com> aazhari at jainconsultants.com
>
> Web: <http://www.jainassoc.com/> www.jainassoc.com
>
>
>
> NOTICE OF CONFIDENTIALITY
> This communication, including any attachments, is intended only for the
> use
> of the addressees and is confidential.
>
> If you received this communication in error, please permanently delete the
> entire communication from any computer or other storage medium.
>
>
>
> cid:image002.gif at 01C92EB4.ADAA2610Please consider your environmental
> responsibility before printing this e-mail & any documents
>
>
>
> _______________________________________________
> Bldg-sim mailing list
> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>
More information about the Bldg-sim
mailing list