[Bldg-sim] U Value
Nick Caton
ncaton at smithboucher.com
Thu Apr 15 07:01:38 PDT 2010
Sambhav,
Don't have my copies of 90.1 handy.. but I think I can guide your questions - do ask again if I'm missing the mark.
1. While your units look about right for a U-value (Btu/h·ft2·°F), baseline underground walls, in 90.1-2004, are defined with a C-factor, not a U-factor. Appendix A section for underground walls explains how it's different from U-factor (I think C basically excludes air films), and has a table you can reference to find a C-value from chapter 5. Between that table and the relevant appendix A text section, you can build a custom construction to match the C-value specified.
2. I don't think there's any specific guidance regarding wall/floor/partition construction absorptance values in 90.1. It's one of those things that fall generally into "match the proposed." 90.1 does specify "solar reflectances" for roofs only, and we handle those (somewhat indirectly) through the absorptance inputs for roof constructions.
Hope this helps,
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of sambhav tiwari
Sent: Thursday, April 15, 2010 6:55 AM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] U Value
Hi All,
What should be U value for below grade walls for basline is it 1.14 btu/hrsqft2F. and how much should i consider absoptamce fro base line below grade walls.
I look forward for your response.
Thanks
Sambhav Tiwari.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100415/c2232a08/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100415/c2232a08/attachment-0001.jpeg>
More information about the Bldg-sim
mailing list