[Bldg-sim] Easy Question 2
Bill Talbert
btalbert at aeieng.com
Tue Apr 13 13:36:14 PDT 2010
If you apply 'addendum a' to 90.1-2004, you don't have to distribute windows evenly across the façade. There are a couple of additional changes in addendum a, including supply air temperature reset of 5 deg F (instead of the original 10 deg F) and a building area change to Table G3.1.1A that would also have to be applied since addenda are acceptable as long as they are applied in full.
BILL TALBERT PE, LEED® AP
SR. SUSTAINABLE ANALYST
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI 53719
P: 608.441.6677 | F: 608.238.2614
btalbert at aeieng.com | www.aeieng.com
-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Eurek, John S NWO
Sent: Tuesday, April 13, 2010 3:04 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Easy Question 2
Easy Question; Ha,
I did not specify which version I was using.
I am on LEED V2.2 hence ASHRAE Standard 30.1-2004.
My question is about interpitation rather than programming but I am using
Trace 700.
(I am still looking for an completed Trace file for LEED so I can see an
example or somebody to offer a good argument to us E-quest so I can purpose
it to management.)
The answer I received to my first question (See below) seemed to be that the
windows are to be spread evenly over the entire building. Every exterior
wall will have the same percent window area (up to the maximum of 40%) Thank
you all for your interpretation.
Second Question:
I plan on modeling the mechanical room, vestibules and stair wells as heating
only. I am in climate zone 5B and according to 90.1-2004 Table 3.1 if the
heating output is less than 15btu/h*ft^2 but greater that 3.4btu/h*ft^2
according to 90.1-2004 section 3.2 definitions it is considered semiheated.
Should I spead the fenestration arcoss the walls of the semiheated spaces?
(I've come to terms with the fact that my server rooms will now have windows
in the baseline.)
Original Question: (has been answered)
I have a two story building. For the baseline I am evenly distributing the
fenestration.
The first floor window area is 462.2 ft^2
The second floor window area is 647.1 ft^2
The first floor wall area is 4858 ft^2
The second floor wall area is 4858 ft^2
In the base line model do I use:
First floor 9.5%
Second floor 13.3%
OR
First floor 11.4%
Second floor 11.4%