[Bldg-sim] Appendix G. laboratory spaces with minimum 5000 cfm exhaust
Paul Erickson
perickson at aeieng.com
Wed Aug 18 13:37:25 PDT 2010
Kevin,
I would suggest that the large loop hole created between G3.1.2.10 (itself and exception h) and your interpretation of G3.1.1 (exception d) does not seem synchronous with the trajectory of 90.1 and ASHRAE's overall goal of reducing energy use in buildings. As I mentioned in my previous post, a few of us (AEI, ASHRAE, Labs21, and NREL) began a dialogue about this in January hoping to get published clarity via the 90.1 Continuous Maintenance process. The timing of our comments happened to coincide with committee voting already in progress and no clarification was made. However, it was discussed that the intent is that the 5000 CFM minimum is in reference to System exhaust rates, not the exhaust rates of a single Space.
If we're not careful and professionally discerning about loopholes like this one (many of which have thankfully been closed due to the efforts of various groups and volunteers through the CM process and committee participation) we are perpetuating the very type of modeling that has led to modeled vs. actual energy discrepancies that have brought so much critique in recent years.
Perhaps your perspective is shared by others and an open discussion on the topic would serve the modeling community well. Thanks for chiming in.
Regards,
Paul
Paul Erickson LEED(r) AP
SR. Sustainable Design COnsultant
AEI | AFFILIATED ENGINEERS, INC.
5802 Research Park Blvd. | Madison, WI 53719
P: 608.236.1112 | F: 608.238.2614
perickson at aeieng.com<mailto:perickson at aeieng.com> | www.aeieng.com<http://www.aeieng.com/>
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Kevin Kyte
Sent: Wednesday, August 18, 2010 3:10 PM
To: Bishop, Bill; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Appendix G. laboratory spaces with minimum 5000 cfm exhaust
Bill:
The answer is in the question, "For laboratory spaces..."
Kevin
________________________________
From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com]
Sent: Wednesday, August 18, 2010 2:42 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] Appendix G. laboratory spaces with minimum 5000 cfm exhaust
For baseline HVAC system type, ASHRAE 90.1-2007 has the following exception (G3.1.1 d.):
"For laboratory spaces with a minimum of 5000 cfm of exhaust, use system type 5 or 7 that reduce the exhaust or makeup air volume to 50% of design values during unoccupied periods."
Similarly, "systems serving laboratories with exhaust rates of 5000 cfm or greater" are excepted from the baseline energy recovery requirement (G3.1.2.10 h.).
When applying this exception, is it 5000 cfm per space? Per floor? Per building? Per system?
Thanks,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20100818/0fbf5cf0/attachment-0001.htm>
More information about the Bldg-sim
mailing list